Hi all.

It has been a long time since I have been on this site asking for advice on central heating controls. But, I now do need some help if possible. I installed a tado v3+ starter kit a little over a yr ago. 3 weeks ago the client called me to tell me the heating wouldn't turn off. I inspected the receiver which seem to be continuously calling for heating without demand. Called Tado and they sent me a new one. 3 weeks later the same fault.

Now Tado have said I need to install a relay to stop the contacts in the receiver welding together when the pump turns on. Now I have installed a few tado controls and never experienced this. They have sent me a diagram of the relay and the wiring, but for the life of me I cannot figure out how to wire this up. Ideally I want it in the airing cupboard with the wiring centre and pump etc (the receiver that is welding is in the kitchen).

Please see the image attached from Tado and one i found on the relay manufacturers website.

The system is a Y plan. Do I take Screenshot_20260114_164622_Email.jpgScreenshot_20260119_211120_Chrome.jpg

Do I take a live and neutral from the wiring centre to A1 and A2 on the relay and then CHNO to 13 on the relay and then 14 on the relay to white wire on the 3 port to switch the pump or do I take it to the orange wire after the valve has switched?

Thanks again if anyone has any advice.

Mutts
 
If the pump is in the boiler, or if there is A pump in the boiler, then the relay has to be added at the boiler. That's where the surge is happening, not in the wiring centre.
The diagram they provide seems to cover what's needed.
If the aim is to protect the Tado wireless receiver contacts, that is exactly where the modification needs to be added.
 
Hi.

Thanks for your reply. The pump is seperate to the boiler and they say they when the pump turns on it is welding the receiver contacts.

Cheers
I think I'm misunderstanding the system, sorry!
I get now that the wiring centre and pump are in the airing cupboard.
The receiver with the load problem is at the boiler. (I wondered if the boiler also had a pump in it, as I'm not entirely clear how the receiver is managing to switch the pump in the airing cupboard)

Is there currently hard wiring between the receiver/boiler and the airing cupboard?
If so you might be able to use some of it to connect the receiver contacts to power the relay coil, and put the relay in the airing cupboard.

Fundamentally the problem you need to fix lives with the receiver. The relay has to be wired directly to the receiver, to power the coil through the troublesome contacts, so the relay contacts take the load..
To do that you need wires directly between the two (or another wireless link!)
 
I think I'm misunderstanding the system, sorry!
I get now that the wiring centre and pump are in the airing cupboard.
The receiver with the load problem is at the boiler. (I wondered if the boiler also had a pump in it, as I'm not entirely clear how the receiver is managing to switch the pump in the airing cupboard)

Is there currently hard wiring between the receiver/boiler and the airing cupboard?
If so you might be able to use some of it to connect the receiver contacts to power the relay coil, and put the relay in the airing cupboard.

Fundamentally the problem you need to fix lives with the receiver. The relay has to be wired directly to the receiver, to power the coil through the troublesome contacts, so the relay contacts take the load..
To do that you need wires directly between the two (or another wireless link!)
Hi there. Thanks for your reply. The receiver is on its own in the kitchen (it replaced a potterton ep2000 programmer). A wiring centre is in the airing cupboard which also has the pump, cylinder etc. So the live, neutral and earth go from the wiring centre to the receiver and then the CH On from the receiver goes back to the wiring centre which connects to a motorised valve which switches to turn on the pump and boiler. I hope that makes sense.
 
Hi there. Thanks for your reply. The receiver is on its own in the kitchen (it replaced a potterton ep2000 programmer). A wiring centre is in the airing cupboard which also has the pump, cylinder etc. So the live, neutral and earth go from the wiring centre to the receiver and then the CH On from the receiver goes back to the wiring centre which connects to a motorised valve which switches to turn on the pump and boiler. I hope that makes sense.
Oh I see. Thanks, that's good.
So, with the Finder relay now at the wiring centre, the "CH on' wire that comes from the receiver needs to go to one side of the relay coil, say A1, and N to A2.
Then connect the Finder relay contact 13 to where the "on' wire previously went, and 14 to perm L.
So the receiver actuates the relay coil, and the relay contacts perform Ch ON to mimic what happened before.
PS there are possibly other ways of doing it, but this seems the most straightforward, and relieves the receiver contacts completely from all loads at the wiring centre.
 
Last edited:
Oh I see. Thanks, that's good.
So, with the Finder relay now at the wiring centre, the "CH on' wire that comes from the receiver needs to go to one side of the relay coil, say A1, and N to A2.
Then connect the Finder relay contact 13 to where the "on' wire previously went, and 14 to perm L.
So the receiver actuates the relay coil, and the relay contacts perform Ch ON to mimic what happened before.
Thanks for this. This certainly makes sense. So this is all before the motorised valve. So CHON goes to A1 and then out on 14 to fire the motorised valve which then switches and connects the pump and boiler.

When I asked AI, it came up with this which I thought was quite reasonable...
 

Attachments

  • 20260119_213622.jpg
    20260119_213622.jpg
    3.4 MB · Views: 13
Thanks for this. This certainly makes sense. So this is all before the motorised valve. So CHON goes to A1 and then out on 14 to fire the motorised valve which then switches and connects the pump and boiler.

When I asked AI, it came up with this which I thought was quite reasonable...
Yes agreed
So CHON goes to A1 (after you connect N to A2) and then (after you connect L to 13) out on 14 to fire the motorised valve which then switches and connects the pump and boiler.

Just wanted you to be clear these are two separate circuits!
What goes to A1 completes a circuit to Neutral, separately from L in on pin 13 going to 14 to fire the motorised valve etc.

Best wishes getting it sorted.
 
Yes agreed
So CHON goes to A1 (after you connect N to A2) and then (after you connect L to 13) out on 14 to fire the motorised valve which then switches and connects the pump and boiler.

Just wanted you to be clear these are two separate circuits!
What goes to A1 completes a circuit to Neutral, separately from L in on pin 13 going to 14 to fire the motorised valve etc.

Best wishes getting it sorted.
Just one question, if I wire it up before the motorised valve, this will only protect the central heating relay (it only seems to be the heating one that has the issue) when the pump fires and not the hot water relay. If I install it like AI has said, can you see this causing any issues? Thanks again for your help.

Thanks again for you
 
Just one question, if I wire it up before the motorised valve, this will only protect the central heating relay (it only seems to be the heating one that has the issue) when the pump fires and not the hot water relay. If I install it like AI has said, can you see this causing any issues? Thanks again for your help.

Thanks again for you
Thats an interesting question. I hadn't thought about potentially having the same problem on the HW side.

You could put the Finder relay contacts just in the supply to the pump (I mean putting supply live to 13 and the pump L to 14, thus the pump current won't be coming from the control side), and feed the relay coil from what was previously feeding the pump, eg orange wire and cylinder stat to A1 and Neutral to A2.
That would save both CH and HW contacts from pump surge current.

Assuming it is just the pump surge that is the problem, this is a better solution!
 
Thats an interesting question. I hadn't thought about potentially having the same problem on the HW side.

You could put the Finder relay contacts just in the supply to the pump (I mean putting supply live to 13 and the pump L to 14, thus the pump current won't be coming from the control side), and feed the relay coil from what was previously feeding the pump, eg orange wire and cylinder stat to A1 and Neutral to A2.
That would save both CH and HW contacts from pump surge current.

Assuming it is just the pump surge that is the problem, this is a better solution!
Thank you for your help in this. I am very grateful. I have attached an "excellent" sketch of what I believe is the best way. Am I getting this correct?
 

Attachments

  • Screenshot_20260121_064953_Chrome.jpg
    Screenshot_20260121_064953_Chrome.jpg
    230.4 KB · Views: 9