shakin2011

39. From Appendix 12 the maximum permitted voltage drop for a 230V singl-phase lighting circuit, fed from the public LV distribution system, is:

[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]A. 20A
B. 32A
C. 45A
D. 50A

and if you would be kind enough to explain how you find it out!!
[/FONT]
[/FONT]
 
i agree, page 358 table 12A

or 230 x 0.03 = 6.9V or 3%
 
Last edited by a moderator:
this are mock exams from ebay, some questions to me dont make sense like this one. why is it asking for volt drop and the answers are in amps.
 
Yes, the answer is 6.9 Volts or 3% for lighting-you appear to have 2 questions in one there!

The maximum volt drop for uses other than lighting is 5% or 11.5 Volts.

Do you have a copy of the On-Site Guide and BS7671:2008 ?
 
you are asking for volt drop but your answers are current?

Agree, think this is a mock question and the wrong set of answers. The other question may be something along the lines of

In a 4mm radial circuit, what mcb/rccb would you use?
A.1%
B.3%
C.5%
D.7%
 
this are mock exams from ebay, some questions to me dont make sense like this one. why is it asking for volt drop and the answers are in amps.


get your money back fella..

these guy's shouldn't really be selling this stuff, and there are hundreds of members on here who can help you out for free.. or if you want to pay us make sure you PM me first
:cool:
 