Spudnik

Hi chaps,

I am having a huge brain block...

Got a Vaillant boiler to wire up to an existing wired system.

Tell me, normal system with 2 valves, room AND tank stat etc...

How would you connnect these up to this?

Terms 3 & 4 require timed ON feed to 3 and switched feed to 4, 5 N

screen-capture-1.jpg
 
Edit........

Actually, just thinking about it, dont i just need to disconnect the link and wire in a switched live from wiring centre into term 4?

Im guessing that term 3 is a 230V feed looped from the boiler perm L?

Goddamit.....

:D
 
Thats how I see it.....just use term 4 as the boiler on trigger from the valves....and a perm L+N.....forget 3 and 5
 
Last edited by a moderator:
Edit........

Actually, just thinking about it, dont i just need to disconnect the link and wire in a switched live from wiring centre into term 4?

Im guessing that term 3 is a 230V feed looped from the boiler perm L?

Goddamit.....

:D


Correct sir.

3,4 & 5 are there for you to connect any external controls to, 3 is your perm live supply out to your roomstat for instance, 5 is a neutral supply out to your stat and 4 would be the switched return from the stat.

As you already have power to the stats & valves etc via the CH JB, all you need is to connect the switched return via the orange cores of the zone valves to terminal 4.

As long as you have a 4 core HR flex to the boiler, Robert will be your fathers brother.
 
Much obliged my learned friends.

I have to say that this job should only have been a couple of days work but has now expanded to over a week.!

Every time I go in there, there is another list he wants doing.

Not complaining but..........