getting my head around downlights and max loadings etc...!
scenario! customer wants 8-10 Gu10 downlights!!
obvious sums = 10 x 50w = 500w (dimmer is Max 400) so NO GO
soloution 10x 35w = 350w (50w under dimmer capacity) (actually going to drop it to 9 lights some how)
bearing in mind customer wants NO wall chasing so cant drop another switch either!! got to utilize existing switch drop and power! and they want to HAVE a dimmer!
next one! when fitting LEDS Gu10's do you use the 4/5w Figure or the equal too 35/50w figure!! i presume the LED one!! plus dimable LEDS are out of question at £25 a pop!