just been to price a job. CU and tails to be upgraded. client has had a recent niceic PIR, so 1st thing was to look at the PIR to see what IR readings had been recorded, can't remember all the mistakes but here's the ones i can.
1. no IR readings recorded.
2. no RCD... code 1.
3. main bonding (6mm) undersized..... code 1.
4. main earthing undersized (6mm).... code 1.
5. shower fuse over sized ( 45A fuse, 6mm cable, 8.5kW shower ).... code 1.
6. no mention of missing fuse cover.
7. no identification of cables at varoius points ... code 2. ( only thing i can see is that the N and E bars in the rewireable wylex are not numbered ).
8. no circuit identification or warning labels... code 2.
i can accept 7 & 8, but all those code 1's.. no way.
OK. now the job i have to quote. 8meters tails from 60A SW. ISOL to CU (client wants 25mm in case he wants to upgrade to 100Asupply in the future. OK, fair enough. can run tails in 2x2 trunking, considered SWA but as the tails are protected at source, i think that allows for standard single tails.
CU is currently 8 way with 3036 fuses, going to fit a 6+6 dual RCD board. MET is in garage by meter . gas meter is local to MET. however, water stop tap is in shower room, just behind the CU. question is, is it acceptable to bond the water to the earth bar in the CU, rather than running back to the MET. it is after all a common point.
1. no IR readings recorded.
2. no RCD... code 1.
3. main bonding (6mm) undersized..... code 1.
4. main earthing undersized (6mm).... code 1.
5. shower fuse over sized ( 45A fuse, 6mm cable, 8.5kW shower ).... code 1.
6. no mention of missing fuse cover.
7. no identification of cables at varoius points ... code 2. ( only thing i can see is that the N and E bars in the rewireable wylex are not numbered ).
8. no circuit identification or warning labels... code 2.
i can accept 7 & 8, but all those code 1's.. no way.
OK. now the job i have to quote. 8meters tails from 60A SW. ISOL to CU (client wants 25mm in case he wants to upgrade to 100Asupply in the future. OK, fair enough. can run tails in 2x2 trunking, considered SWA but as the tails are protected at source, i think that allows for standard single tails.
CU is currently 8 way with 3036 fuses, going to fit a 6+6 dual RCD board. MET is in garage by meter . gas meter is local to MET. however, water stop tap is in shower room, just behind the CU. question is, is it acceptable to bond the water to the earth bar in the CU, rather than running back to the MET. it is after all a common point.