just been to price a job. CU and tails to be upgraded. client has had a recent niceic PIR, so 1st thing was to look at the PIR to see what IR readings had been recorded, can't remember all the mistakes but here's the ones i can.

1. no IR readings recorded.
2. no RCD... code 1.
3. main bonding (6mm) undersized..... code 1.
4. main earthing undersized (6mm).... code 1.
5. shower fuse over sized ( 45A fuse, 6mm cable, 8.5kW shower ).... code 1.
6. no mention of missing fuse cover.
7. no identification of cables at varoius points ... code 2. ( only thing i can see is that the N and E bars in the rewireable wylex are not numbered ).
8. no circuit identification or warning labels... code 2.

i can accept 7 & 8, but all those code 1's.. no way.

OK. now the job i have to quote. 8meters tails from 60A SW. ISOL to CU (client wants 25mm in case he wants to upgrade to 100Asupply in the future. OK, fair enough. can run tails in 2x2 trunking, considered SWA but as the tails are protected at source, i think that allows for standard single tails.
CU is currently 8 way with 3036 fuses, going to fit a 6+6 dual RCD board. MET is in garage by meter . gas meter is local to MET. however, water stop tap is in shower room, just behind the CU. question is, is it acceptable to bond the water to the earth bar in the CU, rather than running back to the MET. it is after all a common point.
 
question is, is it acceptable to bond the water to the earth bar in the CU, rather than running back to the MET. it is after all a common point.

Can't see a problem with that, as long as it's 16mm from the cu to the MET.

Steve.
 
it will be. 25mm L & N , 16mm E. oh, it's TN-S. solid black 10mm from sheath to MET. will be fitting a new MET with bigger holes. the CU at present is fed with 10mm T/E. unsure of the DNO fuse rating or type, its about 1970 in a BILL cut-out. as it's a bit old i don't want to pull the fuse ( do i ever ! ), and re-use the existing metalclad switch fuse. will earth this casing to the met.
 
Last edited:
Dad the same situation on a job earlier this year. Gas bonded to the MET in the garage and water bonded at the CU, CU connected to MET via 16mm earth. Personally I didn't see a problem, but a few others on here said not to do it for various reasons.
 
I can't seea problem. It's just that it's conventional to run all bonding to either 1 or the other. What do you think of the codes the guy gave on the installation?
 
I can't seea problem. It's just that it's conventional to run all bonding to either 1 or the other. What do you think of the codes the guy gave on the installation?

The PIR guy is obviously trying to freighten the client into spending lots of money.

Did you comment on the inappropriate codes in front of the client?
 
I can't seea problem. It's just that it's conventional to run all bonding to either 1 or the other. What do you think of the codes the guy gave on the installation?

Over the top big time. I'm no expert in PIRs, but wouldn't of coded them as he did.

TBH would of probably consulted with the best practice guide to offer a more accurate coding myself.
 
The PIR guy is obviously trying to freighten the client into spending lots of money.

Did you comment on the inappropriate codes in front of the client?

certainly did. explained that code 1 was for an unsafe installation with immediate dangers, and that it had been OK for 40 odd years as it is, so what's the danger? either he was trying to frighten them or needs to go back to school.
 
If that was me i'd have issued a danger notification , perhaps the guy only had 1 finger , tel id put in a bigger board perhaps a hi integrety one reason being the guy said he wants to expand so you'd have plenty of ways then
 
Big firm round here did a PIR for a retired vicar, managed to list the ccts on the form, no other info recorded, charged him £300 said his installation was unsafe due to the junction boxes under the floor. Quoted him seven grand for a rewire.

Bandits

personal preference: One MET, in CU or otherwise all cables to one point.
 
Last edited by a moderator:
If that was me i'd have issued a danger notification , perhaps the guy only had 1 finger , tel id put in a bigger board perhaps a hi integrety one reason being the guy said he wants to expand so you'd have plenty of ways then

going for wylex 15way hi integrity board. £85 + VAT fully loaded. from elec. center. 80A SW fuse off meter as tails are 8m.
 