- Reaction score
- 1,169
How will the adiabatic help?
Sorry Chris, mis-typed on my part, I was thinking of Darkwoods earlier post whilst typing. I will edit my earlier post to maintain clarity
Discuss Downsizing a cable mid-circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I can see the regs you are looking at, and agree the regs should not be taken in isolation.
Reg 433, says shall not be applied to installations situated in locations presenting a fire risk etc...
Iam sorry to have to disagree with both of you here, as a kitchen or other domestic location provides a very real risk of fire in my opinion.
You may be able to use that reg in a different environment and wiring system/containment system, other than domestic.
Iam not saying either of you are wrong per se, but I would not be happy signing that off, as I could not guarantee the conditions required to satisfy parts of 433.
I would much prefer to cover my own backside in this instance.
A very interesting debate none the less.
The reg states its not to be applied to installations situated in locations PRESENTING a risk of fire or explosion
I realise why you left explosion out but i think its key to the meaning too as it gives a kind of category to the term fire risk taking it from low level risk to a higher level as the words are presented together within the sentence, it would be a strange set up to relate and follow a low level fire risk of a kitchen to a explosive risk of a car paint booth.Hi Darkwood,
Yes typical regs, double speak and cryptic lol.
I deliberately left the word explosion out of my answer, as we all agree that does not apply to domestic in the normal sense of things.
As to risk of fire, well that is open to interpretation, I agree the wording of the reg. is not very clear, but I could debate the point that the wiring and containment (or lack of containment) in a domestic situation is not specifically protected against this either.
Hi darkwood,
I understand what Chris and yourself are referring to re: reg 433 wrt to fire risk categories (agreed btw), but I cannot agree on any of the other sections of 433.3.1 in this situation (we know what kitchen fitters are like).
I can find at least two regs which states the 3m rule should apply generally in most cases, and a couple of regs which are debatable in this instance, and depend on certain other conditions been met, which are outside the scope of domestic, on why it need not be.
The other regs which say it need not be provided are for specialised applications/situations.
I said earlier if the OCPD at the origin was suitable for the reduced cable csa, then this need not be a problem, other than the 2m isolation point.
Reply to Downsizing a cable mid-circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net