One should always trip, there are even reasons for redundant protection.
However, in this application as E54 says, just do it right.
If you don't need redundant protection don't bother.
 
Just a question but why can't you configure your circuits so that the greenhouse/shed/outbuiling or whatever it is runs from an rcbo on an unprotected way?

RCD's will remain happy and so will outbuilding and discrimination will not exist :)

Sometimes the perfect solution is not always the easiest to achieve but it does exist one way or another :D Worst case, stick a two way consumer unit (main switch and rcbo) in before the consumer unit) :thumbsup
 
It's just impossible to get a new cable from the CU.

The guy has had all new floors put down and the CU is in a sort of concrete bunker (and so is the main incomer) in the middle of the house.
He's had all sorts of extensions added in an outward direction from this concrete bunker and sealed all the floors with wood laminate.

I'm going to really take my time on this one but as it looks at the moment a new cable is nigh on impossible.

Supply is underground TN-S.
 
Last edited:
Surface mount trunking right the way through the property " Gert Lush" lmao

No such thing as impossible, just means that a sacrifice or two may be required ;)

:thumbsup
 
I will go and do some more testing tomorrow but right now I gotta crash.

Thanks for your help everyone.

I won't be starting this job until after my assessment that's assuming I pass but I will test as much as I can in the meantime.
 
There's always a way. If you can't do the job properly don't do it. A good reputation is hard earned and easily lost.

Do you have any photos of this concrete bunker?
 
I have been doing some testing work on a Nursing Home (new client) which had two 30ma RCDs in series (1 x DB supplying 5 x DB's approx 40m appart) and while testing it was tripping at both RCDs 1 x on one and 5 times on the other really annoying as made testing awkward ! Not ideal.

Back to original scenario of outside supply I always put the outside supply on the non RCD side of the board supplied via a RCBO 100ma and 30ma at shed CU this gives full discrimination for the outside circuit. How do the rest of you do it?
 
I always put the outside supply on the non RCD side of the board supplied via a RCBO 100ma and 30ma at shed CU this gives full discrimination for the outside circuit.

Are you sure about that?

What are you doing when you're testing at x5 on RCD test?

You would need a time delayed RCD as I understand it from reading posts on the forum?
 
The RCD testing was not consistant sometime tripped only on one rcd other times took both out. Yes you are correct time delayed 100ma sorry took that for granted.
 
Back to the OP, if the circuit serving the outbuilding is protected by a 30mA RCD, why bother with a 2nd RCD?
 
Im really intrested in this, anyone got a technical reason or idea why this could happen?


Faulty RCDs? Cannot see any other reason theres no magic secret with them as far as Im aware. Needasparks what do you mean you had discrim. with two 30mA RCD's?
 