Discuss RCD's in series in the Australia area at ElectriciansForums.net
There's always a way. If you can't do the job properly don't do it. A good reputation is hard earned and easily lost.
Do you have any photos of this concrete bunker?
I have been doing some testing work on a Nursing Home (new client) which had two 30ma RCDs in series (1 x DB supplying 5 x DB's approx 40m appart) and while testing it was tripping at both RCDs 1 x on one and 5 times on the other really annoying as made testing awkward ! Not ideal.
Back to original scenario of outside supply I always put the outside supply on the non RCD side of the board supplied via a RCBO 100ma and 30ma at shed CU this gives full discrimination for the outside circuit. How do the rest of you do it?
Are you sure about that?
What are you doing when you're testing at x5 on RCD test?
You would need a time delayed RCD as I understand it from reading posts on the forum?
Im really intrested in this, anyone got a technical reason or idea why this could happen?
Faulty RCDs? Cannot see any other reason theres no magic secret with them as far as Im aware. Needasparks what do you mean you had discrim. with two 30mA RCD's?