Currently reading:
Two Three Phase motors on one Overload
Discuss Two Three Phase motors on one Overload in the Electricians' Talk | All Countries area at ElectriciansForums.net
T
TailSpin
Hi All
I have come across two 3 phase in line WOODS fans rated @ 0.22 kW / 0.6 amps connected together on one overload. This does not seem correct is there anyway this could be right ?
Regards
Tailspin :shocked::confused:
Woods dual impeller fans were often connected like that. It’s 20 odd years since I worked on them. If your worried about it change it for one contactor with two O/L units but if it’s a Woods own brand starter, best of luck! They were tight on space at the best of times.
It’s important that they start and stop together so one contactor with two O/L units is the best way.
Hi All
Regards
I don't think motors < 0.37kw require overloads yet this setup offers phase loss/imbalance protection and overload indication.
What is the overload set to?
As memory serves, that’s the basis of the original Woods starters.
Basically keep it simple.
The ones I worked on dated from the early 50’s (just older than me before you lot start), the only time they failed was when a kiln backfired and the fan motors got fried.
I would have said it was roasted more than fried:yes::teeth_smile:
Hi all
Thanks for your thoughts . Overloads are rated for both to run together I was wondering if any regulations are in place to avoid running more that one motor on one overload ?
Regards
John
All of the overloads are Alan West : controlled by
Enbray contactors .
This set up is used through out the site for AHU extract and supply fans.
Regards
Tailspin
Christ, are you working in a museum?
How long have these motors been like that? Are they working OK?
Unless you’re trying drum up business for unnecessary work, leave it alone.
Reply to Two Three Phase motors on one Overload in the Electricians' Talk | All Countries area at ElectriciansForums.net