Can someone please explain to me how the Rating of RCD work because I've read on different forums that you can not exceed the rating of the RCD ie 63A or 80A if that's the case why do C.U like 10 way dual RCD, have a total MCB rating of 218 A if all MCB was used and only 143 total A for the RCD's, surly maximum demand comes into play.
 
Last edited by a moderator:
Can someone please explain to me how the Rating of RCD work because I've read on different forums that you can not exceed the rating of the RCD ie 63A or 80A if that's the case why do C.U like this one

http://www.*************/p/volex-10-way-dual-rcd-split-load-consumer-unit-10-mcbs/54467?cm_mmc=GoogleBase-_-Datafeed-_-Electrical and Lighting-_-Volex 10-Way Dual RCD Split Load Consumer Unit %26 10 MCBs

have a total MCB rating of 218 A if all MCB was used surly maximum demand comes into play.

You'll get more sensible answers on DIYnot.com than here!
 
gets worse, my house only has a 63A fuse supplied by DNO, my shower, oven, kettle and microwave on their own take more than that - why has it not blown ?
 
so why are some sparks telling me I cant use maximum demand for RCD one guy was even telling me you can only have a maximum of 3 MCB of an RCD
 
why is my question to basic

OK...
the 63 or 80A ratings are the maximum in service current capacity of the device, more than that and they'll start warming up.
The crucial figure on a RCD is the mA value. RCDs are for additional protection to disconnect supply on the event of earth leakage faults.
 
I know what an RCD does and I've always used maximum demand but when some called professionals have a completely different point of view to mine it makes me question what im doing obviously it would be impossible to protect an installation form earth fault if I didn't use maximum demand
 