Thanks Biff and sorry again if I didnt explain myself properly.Your builder is right , as a sub-mains to the flat , the earth in the T&E cable is fine.
The only earth that needs to be 16mm is the conductor from the MET to the switchgear at the supply position.
So just to confirm, 16mm from MET to isolator (which I presume there is one).
Thanks again and have a great weekend,