S
s.keech
Hi can some one help. Just starting out and have passed level 3 guilds have been asked to fit a fan and downights in a bathroom. I know it is notifiable but can any one tell me how to r.c.d everything. Is the cheapest way to fit r.c.d fused connection unit outside bathroom or do i have to run new circuit from c.u. If i can use R.c.d outside bathroom do ileave the 13 amp fuse in it or change it.
Cheers for any help
Steve
depends on what board you have old rewireable Split load dual RCD etc etc you wouldnt use a 13amp fuse on fans or lights it would be a 3 amp , and bonding must be installed to incomming services water gas oil etc its not just adding a few lights some more information would be good ,IE board type fuses or mcb's with RCD protection then i may be able to help further
The Regulations require that the circuit be protected.
That means the whole circuit, not just a part of it.
As such the RCD protection would have to be at or very near to the origin of the circuit which is at the DB/CU.
It has also recently come to my attention, that the manufacturer's do not consider RCD FCUs as being suitable for fixed wiring.
so that would mean running a new circuit just for the bathroom then. is there not an easier way
No not at all RCD the whole circuit seperate board with an RCD on it , but like i have said what is the current protection , fuses mcb's etc
Spin, out of interest why do the RCD FCU's get sold then?
I have to admit to using RCD FCU's - there are times when its the only way to get near to the regs.
You do not have to rcd the whole circuit, just the part you are altering and anything down river from it. My niceic inspector confirmed that for me. I always use this method when the cu is too old for a rcbo and the customer too tight to have the cu changed
He not installing the whole circuit, just adding to it....? I'd be interested to see the black & white on that one, in this case common sense ( my common sense) is telling me that protecting the addition with a 30mA Rcd means, well, what I have done, is protected. And not some cobblers someone else may well have done and Im not being paid to look into?
Spartykus.
Do you agree that the Regulations require RCD protection for circuits of locations containing baths and showers?
If not, no worries.
If you do, can you explain how only protecting part of the circuit complies?
Something else, that it appears many are not aware of.
Is that if only part of the circuit is protected, then current from an earth fault on the unprotected part of the circuit will by pass the RCD and enter the location.