Spartykus.
Do you agree that the Regulations require RCD protection for circuits of locations containing baths and showers?
If not, no worries.
If you do, can you explain how only protecting part of the circuit complies?

Something else, that it appears many are not aware of.
Is that if only part of the circuit is protected, then current from an earth fault on the unprotected part of the circuit will by pass the RCD and enter the location.

A point has been made before BUT I'd say that adding a RCD FCU is better than no protection, and also it can help when complying with fan manufacturers requirements to fuse down to 3A.
 
Spartykus.
Do you agree that the Regulations require RCD protection for circuits of locations containing baths and showers?
If not, no worries.
If you do, can you explain how only protecting part of the circuit complies?

Something else, that it appears many are not aware of.
Is that if only part of the circuit is protected, then current from an earth fault on the unprotected part of the circuit will by pass the RCD and enter the location.


Hmm.

I don't disagree with you, but...!
 
I guess at the end of the day, it's down to the individual to make their own choice.
I would not be able to justify installing an RCD in such a manner that it did not offer as much protection as possible.
 
Spartykus.
Something else, that it appears many are not aware of.
Is that if only part of the circuit is protected, then current from an earth fault on the unprotected part of the circuit will by pass the RCD and enter the location.

If the earthing is correct it will not. if done right it will flow down the cpc to the db earth and cause the the mcb or fuse to operate. as the unprotected side will be before the rcd. i cant imagine it going the other way unless the impedance is too great and a earth path exists in the bathroom with a lower impedance.
 
If the earthing is correct it will not. if done right it will flow down the cpc to the db earth and cause the the mcb or fuse to operate. as the unprotected side will be before the rcd. i cant imagine it going the other way unless the impedance is too great and a earth path exists in the bathroom with a lower impedance.

The current will take any available path, not only will it flow back to the origin of the installation, it will also enter the location.
Yes hopefully the OCPD will operate within the specified time of 0.4s.
However the Regulations now require the use of a protective device with an operation time of 0.04s, specifically an RCD.
 
Not really sure.
Yes Handysparks, here's a link to the Beama RCD handbook: RCD Handbook updated - BEAMA | News.
There's a little chart on page 26.

Thanks, spin.
Interesting chart. You're right, it does show that a FCURCD is not recommended for protecting fixed wiring. However is also says that it IS suitable as an outgoing device on a CU or DB and that it IS suitable for protecting socket outlets of 20A or less. About the same level of ambiguity as the wiring regs then!
 
I remember having a long discussion with my college tutor (former ECA inspector) about RCDs in bathrooms.

I had always been of the understanding that I only have to RCD protect the circuit being worked on (ie: if installing a shower, protect the shower radial and go home) but he told me that I'd have to make sure the lighting circuit (at least the bathroom section of it) was RCD protected too.

I will never understand exactly why...
 
People think my interpretation is over the top.
I think that that particular misunderstanding is due to the wording 'all low voltage circuits of the location'.
Some interpret that to mean, that if you work on one circuit, not only must you provide RCD protection for that circuit, but for all.
 
Ok.

However.

In the real world, I know many will continue to protect, for example, the bathroom fan (in line) in the loft that supplies the bathroom with an RCD spur as a cheaper solution, based on real life cost pressures. Note Im not pushing it as right or good; neither am I saying it is wrong. Simply that I believe many will see it as a solution that makes a home safer.

The other point being whats installed is protected by an RCD. If something went wrong i'd be suprised if there was any comeback on the contractor concerned. Given the example above.


This point has been covered in many threads- the idea of leaving an install better than when one arrived.

In way of placation & to avoid being beaten senseless in electrician forum cyberspace(!) i do agree however that simply protecting the whole circuit at source is the best idea. In theory! In practise it may turn a £120 job into a much bigger, moretime consuming, and therefore unacceptable-to-the-client job!!
 
Rcd spur in the loft protecting the bathroom (new circuit from distribution board for bathroom :smilielol5:you having a laugh!!!
 