C
craigj85
Yesterday I was doing an rcd test on a lighting circuit fed via an rcbo 30mA switched by a PIR. I was doing the test at the fitting with the lights on but I was only getting >400 mS? Not sure if I was doing the test correctly or if my testers are playing up?!
Did you try bypassing the PIR, not sure the RCD would be too effective with that in the circuit.
Why don't you just do the test on the load side of the RCBO?
Interesting one, this. Are we testing the response times of the RCD that protects the circuit, or are we testing the response times of an RCD protected circuit?
There is no obligation to test the RCD's at the "ends" of each circuit, but I often do, but there are times I don't
The RCD test is there simply to test the RCD itself, not the circuit connected to it, but like Murdoch there are times when I have performed the test at the end of a circuit. However, if you've measured the EFLI of the circuit then it surely isn't necessary?
ehmm...really?....has the O/P mentioned the earthing arrangements?...
ehmm....really?.....No, but I'm trying to be helpful....I assume the circuit has a CPC! Just saying that I wouldn't be doing the RCD test at the fitting, that's all. Sorry I spoke! ;)
Thanks for replies yes testers we're set at 30mA. I've always thought the test had to be done from a point in the circuit but yes testing at the rcd itself just to get the operating time of that rcd makes sense. It's a minor works cert required by the council for every bit of work we do
Worms; Can; Shut.
is there any load current specification on rcd if it is connected via mcb,for example the attched picture what should be the rating Capture.JPG
the RCD load rating must be higher than the design current of the circuit it's protecting.
I know electricians who when doing a PIR/EICR put down on the form that the RCD must be derated as it is rated at a current rating than the CPD, I wonder at times whether they are compotent or not.