Just been looking at results:
Shed - how can you have a R1+R2 of that low and a Zs that high?? Hes misplaced the . I think! - He also states a 30mA RCD is installed on the shed - when clearly its not!
Hob - That must be one short run - less than a meter with 0.02ohms for R1+R2
Lights - as said above clearly C6 is longer with more points so how can it be the same value as downstairs??
Cooker - Same situation as hob - very short!
Also Zs and Ze they dont match up - considering Ze is 0.27 how can you have 2 circuits at 0.24 showing a Ze of 0.22 (though calculation) and some over circuits showing a Ze of 0.28 - I know bonding can bring it down and up but not by this amount.
I am wondering has he cooked the results??
Also all IRs - am I not right in saying that a reading of >200 Mohms is normally received from someone testing at 250v DC and not 500v DC??