I've been asked to look at putting a new supply to a pool for a heater. It's a long run and there's currently a 1.5mm SWA to run the pump.

We're being asked to quote on a 16A heatpump or similar and they've been told that to up the current carrying capacity for the supply cable they should put a 400v transformer at each end of the run, the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.

I've never heard of this approach, has anyone done something similar?
 
Well in theory it may just work, after all HV transmission works on very similar principles, higher voltage transporting less current.

I have to admit that I have never personally done anything like this, and well I suppose there is more than one way to skin a cat. I would love to see some figures on this
 
I've been asked to look at putting a new supply to a pool for a heater. It's a long run and there's currently a 1.5mm SWA to run the pump.

We're being asked to quote on a 16A heatpump or similar and they've been told that to up the current carrying capacity for the supply cable they should put a 400v transformer at each end of the run, the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.

I've never heard of this approach, has anyone done something similar?


Yes but not in a bloody garden!

Before you go any further concider the cost of two transformers as against the correct cable. Then you will have the earthing of the secondary output of the remote transformer to contend with. Current inrush will be a problem with two transformers. Finaly to use the exsisting cable i would be looking at 660V.

Has the client got deep pockets? If he has tell im to employ a landscape gardener to repair the damage done putting the correct cable in.
 
Sorry got my numbers wrong, it's a 12kw output HP (allow 3.5-4kW input) + the pool pump/filter 500-800w so the demand is only say 5kW...

That makes more sense...
 
if you are going to that trouble why not go all the way and step up to 11kv that should counteract any losses in the cable,if you can get them use transformers with on load tap changers that way you can adjust to compensate for any difference in voltage outside your needs.
 
I've been asked to look at putting a new supply to a pool for a heater. It's a long run and there's currently a 1.5mm SWA to run the pump.

We're being asked to quote on a 16A heat pump or similar and they've been told that to up the current carrying capacity for the supply cable they should put a 400v transformer at each end of the run, the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.

I've never heard of this approach, has anyone done something similar?


Not to boost the CCC of a tiny 1.5mm SWA cable i haven't!! lol!! The cable was too small when it was first installed, for the type of distances your talking about. I take it there is a good few metres to add to that 50m either side of this playground?? Is this installation for a school of some sort??
 
Not to boost the CCC of a tiny 1.5mm SWA cable i haven't!! lol!! The cable was too small when it was first installed, for the type of distances your talking about. I take it there is a good few metres to add to that 50m either side of this playground?? Is this installation for a school of some sort??
Well mate you,ve disappointed me!we are all taking the mick in a roundabout way and then you come on and don,t even mention earthing.how disapointing lol.
 
Well mate you've disappointed me!we are all taking the mick in a roundabout way and then you come on and don,t even mention earthing.how disappointing lol.



The scenario is in my opinion a none starter, so no point in going into the earthing side of things.... lol!!
 
...the idea for this being that this will be cheaper than upgrading the cable and digging up 50m + of playground.
Don't you have directional moling contractors in he UK?

We installed transformers for remote pump and booster station supplies before and it's a very expensive exercise. It will only be worth it if the playground repairs will for some reason cost an arm and a leg or if the distance is over a kilometer.

Edit.
Why did they suggest 400v? You may as well go 1kV if the SWA is rated high enough.
 
Okay, okay, easy chaps... we also run 1kV under low voltage regs. I'm sure we're not to a volt or two amongst friends :)
 