K

kkkkk

Rangemaster oven 15/16kw with 7 to 10m run of cable, specifies to use a 45A rated cooker circuit breaker - we would use one with a socket.
Can be 6mm or 10mm cable, depending on which cooker connections one uses.

Would it be better to use the 10mm cable, and would the MCB be 45A rated, or should it be larger?

Thanks muchly

kkkkk :) :) :)
 
well for a start....you know what OPD your using....you state that at #1
you know your OPD is there to protect your cable.....
so do the maths.....
PS....volt drop wont be an issue over that length of run.....
 
Rangemaster oven 15/16kw with 7 to 10m run of cable, specifies to use a 45A rated cooker circuit breaker - we would use one with a socket.
Can be 6mm or 10mm cable, depending on which cooker connections one uses.

Would it be better to use the 10mm cable, and would the MCB be 45A rated, or should it be larger?

Thanks muchly

kkkkk :) :) :)

Are you talking about a ''Cooker Control Unit'' CCU or the protective device (MCB) in the CU?? From your OP i am thinking you may well be talking about a 45A Cooker control switch with a socket outlet.

If the cooker is rated at 15KW, the supply cable only needs to be 6mm, and the protective device 32A...
 
Hi Engineer54, Yes, I am talking about the CCU with the socket being 45A.
So the cable only needs to be 6mm, and the MCB 32A?
Thanks very much - the only thing that confused me is that the CCU is 45A, so should I match that or go larger.
:) :) :)
 
Hi Engineer54, Yes, I am talking about the CCU with the socket being 45A.
So the cable only needs to be 6mm, and the MCB 32A?
Thanks very much - the only thing that confused me is that the CCU is 45A, so should I match that or go larger.
:) :) :)

Your never going to pull 45A on a 15KW cooker, besides the CCU is only a means of isolation, a simple DP switch. The next size up i believe is 63A and is mainly used for commercial/industrial kitchens and not many manufacturers make them...

Is this a new cable installation, or are we referring to an existing 6mm T&E installation with existing CCU?? If existing leave and use the cable as is. The connection from the CCU to oven can be made using the same 6mm T&E cable, either direct or via a cooker connection wall plate... It's been done like this for around 60 odd years, so your in good company!! lol!!
 
Hi Engineer54, this will be a new cable installation, and a new CCU, in a house extension, and also a replacement Consumer Unit, as the last one suffered from melting damage on the main switch from an assumed loose connection. I am probably going direct from oven to CCU, unless the householder says otherwise. I am also wiring in some new lights - the customer has his own T&E cable of 1mm size (though I prefer 1.5mm, I believe this to be acceptable with 1mm). And two showers, probably 9.5kw, which I have calculated to be 10mm cable for one, and 6mm for the other, due to the difference in length of run (about 15m and 10m respectively). I am sitting my 2382-12 this month, and hope to certificate this one myself. :) :) :)
 