Hi need advise on cable 25 meters run underground for additional consumer unit in garden outbuilding to acomodate 9Kw sauna heater 10kw water heater 3double sockets 6 down lights and 4 outside lights?Thanks in advance .
 
25mm. that should do. a separate supply might be a good idea.
 
Your service head (supply from the network) may not be sufficient to feed an extra load of that size.
 
yeah, well from you posted, you need 100A supply. don't think the average house supply can take that much extra load, unless they got 3 phase.
 
yup agree with 25mm2, however without getting the BGB out now haha, come on it is Christmas eve, I suspect a16mm2 may will do the job, well maybe, but 25mm2 sounds right and what I would put in.
 
i'd be starting with an assessment of any spare capacity at the supply before thinking about cable sizes.
 
agree with biff, although 25mm2 is right, well probably right it is best to consider the capacity, too many beers and a thick head is clouding the judgement at the moment haha
 
And how to consider the capacity ?what i can do is only wire cables but not connecting them .I was suggested Henley on main incoming 100amp then 25mm armoured cable. But know Consider capacity??
 
A few questions for you....
Find out if the water heater will be used simultaneously with the sauna??
I'm taking it that this would be an electric shower type load??
What sort of loads are going to be supplied by the socket outlets??
What sort of outside light fittings, eg, not halogen 500W floods i hope...lol!! ??
What earthing arrangement do you have??
 
And how to consider the capacity ?what i can do is only wire cables but not connecting them .I was suggested Henley on main incoming 100amp then 25mm armoured cable. But know Consider capacity??

You wire this supply then you are responsible for the design included expected demand on existing etc etc .... if the main cutout was to operate because you hadn't taken into account the load demand then you could be liable for all costs relating to the rectification and DNO callout.
P.s. just because the cutout carrier may state 100amps dosn't mean the fuse within is that rating so at some point here you will need to liase with the DNO to so the allowance you have to start with.
 
Yet another chancer with not a clue what he's doing.
Look is not your business chancer or not I'm asking because half electricians I called to give me quate came with lots of bul...et you need that and you need that because law states this is how should be and at the end they want 1000 for two days work it's ripp off because I know basics
 