Hi all
Ive come across an 80a 30ma rcd in a 2 way consumer unit used as the main switch supplied with 25mm tails, am correct by saying this is ok, anyone think otherwise
 
I take it, that these are not the only circuits in the installation.
That there are other circuits connected to another CU.
If so then yes it is acceptable.
 
I can't see anything wrong using an appropriately sized DP RCD as the main isolator for a CU. If were talking about a 16th edition type CU.

If a 17th dual 30mA CU, it would need to be an S type 100mA or similar, if being used as the CU's main isolator!!....

Ooooops, just read the OP again, he's talking of a 2 way Cu!!! So what others have stated above!! lol!!
 
well then its OK....as spin has told you...

P.S. what made you think there was a problem with this?:redface:
 
you could use an s type 100mA as main switch on a 17th ed. split board. esp. if it's a TT earthing arrangement. this would give additional fault protection whilst having discrimination with the 30mA RCDs.
 
Ok just wasnt sure an rcd could take the place of a main switch thanks guys

The switch on an RCD will conform to the same isolator switch requirements, in terms of rating and open contact distances. When you think about it, it does exactly the same job, albeit with a protective element incorporated!! ....
 
Excellent, why would 17th edition cu have to have s type rcd
S type or time delayed RCDs are used to provide discrimination...
so for example, lets say you want to feed a garage with an armoured sub....
and the earthing arrangements are TT...so RCDs are classed as fault protection for TT systems yes...
so you need to provide 30mA for fault at the garage board yes....but your sub also needs fault protection yes...
so you would feed the sub for the garage of ov an 100mA s type top end....
30mA RCD in the sub board and this would give you the discrimination against accumilated earth leakage....
 