I am just learning: If I where to install just radial circuit for example or a fused spur socket, would I have to do a full periodic inspection of the house installation?
 
You would have to issue a ceificate but think about which one! What would you normally issue a PIR (EICR) for?
Have a look again in the regs book or GN3.
 
I am just learning: If I where to install just radial circuit for example or a fused spur socket, would I have to do a full periodic inspection of the house installation?

You could do, but you'd go out of business pretty quickly. :-)
Check Main Earth and Main Bonding Conductors are present and correct, do job and issue a MWC.
 
Would the case be if you think the instillation is not at its best, then you could recommend one to the customer?
 
I am just learning: If I where to install just radial circuit for example or a fused spur socket, would I have to do a full periodic inspection of the house installation?

I would say.... don't install that spur until you know the regs, and don't just guess.
 
It say in GN3 page 60 "after alteration or additions to the original installation"
So Archy Styrigg could be lible if any thing went wrong with his installations.
Am I be correct?
 