The second one in 12months? This time on a garage wall, hidden behind a load of rubbish!

You measure the insulation resistance at 240v across N&E on the associated circuit and it reads very low (<10k). If you are doing work like a CCU update, then you usually start looking for a wiring fault??? Well the rcd skt may well be causing it, so replace it with a normal socket if there's rcd protection already upstream - assuming you know it's there in the first place!

The one last week was made by Powerbreaker and cost me 2hrs wasted time taking sockets of the walls to see if any were n/e shorted.

The better ones don't appear to be a problem - think it's it's associated with the internal test button circuit because when I held the test button in, the N/E short disappeared? Then I dropped it onto the floor at high speed and somehow it shattered:(
 
I've seen many RCD sockets giving very low IR results, so make a point of looking for them prior to a CU change and including removing them as part of the job, and doing so before IR'ing the circuit.
 
I'll be a little bit more pro-active in future I think , like you Murdoch - will ask customers beforehand if they think they have any - not that they'll always know what I'm on about!
 
I'll be a little bit more pro-active in future I think , like you Murdoch - will ask customers beforehand if they think they have any - not that they'll always know what I'm on about!

Not all know what a RCD socket or FCU is but I walk around a property with a client asking where switches, sockets, are, etc......
 