Octopus
am i missing something
sorry ?
Come back and post a thread when you have confirmed continuity of the 3 cores from the board to the first light!
am i missing something
sorry ?
Come back and post a thread when you have confirmed continuity of the 3 cores from the board to the first light!
i think the fact that i have it leaving board and not at the firswt light pretty much confirms theres a break
i think the fact that i have it leaving board and not at the firswt light pretty much confirms theres a break
:S care to explain
I doubt he does tbh.
yet ANother I unsubscribe from!
Its not rocket science. With a continuity tester test for you break.. R1+R2 or R1 + RN and RN +R2. surley that should confirm what the break is. After which Is correcting..
I fail to see what you a struggling with bud
Screwfix for you my boy! and no tea,off you go .........
If this is a wind up then seriously do one.. Had enough over the last day or so of these idiots..
If its genuine.. Take the advice that everyone has given you and test with a proper tester to determine is you have a break and if so what are and where it is.
Sounds like this guy is paying top dollar for you to turn up and determine a fault with only a volt stick...
If you were working on my house id be pretty peed off if you turned up and either 1) didnt have the relevent test gear to test or B) know how to use it to fault find..
Either take the advice or disappear to screwfix forum