Ah, so RayGalea, your saying that if there is a secondary return, which there is, a bronze pump, that it will only let one pump work in conjunction with the bronze pump?
 
Yes , with the pump over run which is a pump feed back from the boiler , can only bring on 1 pump , because either heating or hot water valves are open
 
So, the customer wants the heating and hot water at the same time, is there a way I can achieve this with the secondary return? they don't care what I have to do to acheive this
 
You have 2 systems in effect , working from 1 boiler , I think that 1 off the pumps would have to be removed and flow from the boiler fed through just 1 pump then split to feed the 2x 2 port valves , so plumbing would need to be altered , also check to see if both2 port valves are spring return ,( usually are ) then wire the system as a S plan as normal .
So some plumbing is involved , Simply return it back to an S plan system ......
 
Another thought , are the 2 pumps different sizes, it could be that the pump required for the heating circuit is too highly rated for the hot water circuit and has a smaller pump for the hot water
 
You have 2 systems in effect , working from 1 boiler , I think that 1 off the pumps would have to be removed and flow from the boiler fed through just 1 pump then split to feed the 2x 2 port valves , so plumbing would need to be altered , also check to see if both2 port valves are spring return ,( usually are ) then wire the system as a S plan as normal .
So some plumbing is involved , Simply return it back to an S plan system ......
I think you're barking up the wrong tree here mate. The clue is in the OP stating that the HW pump is a bronze one. These are typically used in conjunction with extra 'return' pipework to circulate the DHW around the house so that hot water is instantly available at each tap without having to draw off some cooler water first. It's nothing to do with the primary circulating water. I would expect this bronze pump to be on a timer, so that instant hot water is available whenever the users are likely to want it.
 
So you've worked lots of heating systems? Not come across a relay? Don't take on work you're not competent to do.
 
Regarding relays on heating systems...
One of the original types of mid position valve used to have a separate relay, forget the make.
Also few years back I did a heating system which consisted of three different zones plus hot water etc and various pumps and that required the addition of several relays. It were A reet bugger. Spent a while working it all out, finished it off and on packing up found the schematic for the system in the back of the boiler manual !
So might pay to start by having a look at any info the householder might have, boiler manuals etc.
 