was looking at a motor the other day and when I measured across all I got was 230v to Earth but not 400v between.
 

Attachments

  • image.jpg
    image.jpg
    207.8 KB · Views: 167
What controls the motor? .... DOL, VSD, Star/Delta, Soft Start etc etc?
Has it got speed control?
What meter are you using to get your voltage?
What's the nature of this post... is something wrong with the motor or its operation?
 
The links are arranged in star formation. If you measure between each incoming phase to the star point of course you're only going to get 230V. That is of course assuming direct connection to the supply. What voltage are you getting between the incoming phase terminals? How is the motor started?
 
What controls the motor? .... DOL, VSD, Star/Delta, Soft Start etc etc?
Has it got speed control?
What meter are you using to get your voltage?
What's the nature of this post... is something wrong with the motor or its operation?
I know nothing about controls and motors. I measured 400v at isolator , which then goes to id say is a starter of some sort (pic). I then measured 230v at motor housing. I used martingale gs38 tester image.jpg
 
Last edited:
I know nothing about controls and motors.

Sorry, but having said that !!
What exactly are you trying to achieve here ??
I think you should put that cover back on to be honest and get someone with you who does know about motors and control gear.
 
Guys and divas , I only check power at devices after that the boss sends it back for specialist which I asumme in this case is an electrical engineer .
 
If it's supplied by a variable frequency drive there's a good chance your tester won't be able to make sense of the supply at the motor due to the high carrier/switching frequencies.
 
If it's supplied by a variable frequency drive there's a good chance your tester won't be able to make sense of the supply at the motor due to the high carrier/switching frequencies.
I measured 230v at all points on motor to earth but nothing between connections
 
Guys and divas , I only check power at devices after that the boss sends it back for specialist which I asumme in this case is an electrical engineer .

If you don't understand the basics of motor control then how do you know what you are testing for or what test equipment is appropriate/safe to use?
 
Its not a drive in the picture, the circuit board looks like some sort of RC circuit, could be for soft start or noise suppression. Any wiring diagrams?
 
It's not a drive and it's a bit elaborate for a suppression board plus there's no ground on it. Maybe soft start but I can only see 2x components on the heat sink so also unlikely.

You didn't say if the motor was running or not. What was the fault they reported and what was the application or machine it was a part of?
 
My tying is too slow, it's probably the control board for the interlocks / estop etc. In that case the motor looks like it's direct on line so I give up about your weird test results in that case.
 
But as said why only getting 230v motor connections,

why nit not just break live with e stops , forget control boards ...
 
The fault was bandsaw not working. It also has a dust extractor tapped off it

1: Determine make and model of said saw.
2: Ask Maintenance if they've got a manual for it.
if not,
3: Get online and see if you can find one.
if not .......
 
The only explanation of getting 230v from all terminals to earth and 0 v between the terminals themselves is that there's only asingle phase being supplied to the motor. That's the easy bit, the difficult bit is figuring what's causing that condition. Maybe the contactor was not energised but one of the contacts is welded closed due to a fault current that occurred previously but then the question becomes what was the earth or the s/c fault.
 
The only explanation of getting 230v from all terminals to earth and 0 v between the terminals themselves is that there's only asingle phase being supplied to the motor. That's the easy bit, the difficult bit is figuring what's causing that condition. Maybe the contactor was not energised but one of the contacts is welded closed due to a fault current that occurred previously but then the question becomes what was the earth or the s/c fault.

Just going to ask if he'd checked the fuses:icon12:
 
Which fuses Ipf ? On the circuit board? Yes there's one which Belleyed out.

theres 400v at dol starter but only 230v at motor casing.

when you hit the start button , the extractor kicks in, the pulls out again and there's a burrRRrr sound but blade don't rotate.

and believe me when I say I ain't fixing this . But would love too some day lol
 
Last edited:
Which fuses Ipf ? On the circuit board? Yes there's one which Belleyed out.

theres 400v at sol starter but on 230v at motor casing

Fair do's.....but we're all guessing a bit at fault finding without being on the spot.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

i=p/u

Arms
-
Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Starters and motors
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
51

Thread Tags

Tags Tags
motors

Advert

Thread statistics

Created
i=p/u,
Last reply from
netblindpaul,
Replies
51
Views
5,077

Advert

Back
Top