Starters and motors

Discuss Starters and motors in the Electricians' Talk area at ElectriciansForums.net

i=p/u

-
Arms
Reaction score
800
was looking at a motor the other day and when I measured across all I got was 230v to Earth but not 400v between.
 

Attachments

  • image.jpg
    207.8 KB · Views: 167
What controls the motor? .... DOL, VSD, Star/Delta, Soft Start etc etc?
Has it got speed control?
What meter are you using to get your voltage?
What's the nature of this post... is something wrong with the motor or its operation?
 
The links are arranged in star formation. If you measure between each incoming phase to the star point of course you're only going to get 230V. That is of course assuming direct connection to the supply. What voltage are you getting between the incoming phase terminals? How is the motor started?
 
What controls the motor? .... DOL, VSD, Star/Delta, Soft Start etc etc?
Has it got speed control?
What meter are you using to get your voltage?
What's the nature of this post... is something wrong with the motor or its operation?
I know nothing about controls and motors. I measured 400v at isolator , which then goes to id say is a starter of some sort (pic). I then measured 230v at motor housing. I used martingale gs38 tester image.jpg
 
Last edited:
Guys and divas , I only check power at devices after that the boss sends it back for specialist which I asumme in this case is an electrical engineer .
 
If it's supplied by a variable frequency drive there's a good chance your tester won't be able to make sense of the supply at the motor due to the high carrier/switching frequencies.
 
I wasn't entirely sure what that was in the pic. Have you got another pic taken from a bit further away?
 
If it's supplied by a variable frequency drive there's a good chance your tester won't be able to make sense of the supply at the motor due to the high carrier/switching frequencies.
I measured 230v at all points on motor to earth but nothing between connections
 
Guys and divas , I only check power at devices after that the boss sends it back for specialist which I asumme in this case is an electrical engineer .

If you don't understand the basics of motor control then how do you know what you are testing for or what test equipment is appropriate/safe to use?
 
It's not a drive and it's a bit elaborate for a suppression board plus there's no ground on it. Maybe soft start but I can only see 2x components on the heat sink so also unlikely.

You didn't say if the motor was running or not. What was the fault they reported and what was the application or machine it was a part of?
 
My tying is too slow, it's probably the control board for the interlocks / estop etc. In that case the motor looks like it's direct on line so I give up about your weird test results in that case.
 

Reply to Starters and motors in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top