I have an NICEIC inspection in a few weeks for which I am replacing a cu.
The lighting circuits have no cpc and on doing the risk assessment I have found five class 1 lamps with metal shades. The rest of the lamps are class 2.
Is it obligatory to replace these units for the inspection or is it...
Hi new to pat testing just got Fluke 6500 tester and was wondering the process for testing a hard wired appliance like a dishwasher which has a spur switch above work top.
also class III testing on the fluke can anyone explain as there does not seem to be a pre set test
thanks
when pat testing class 2 equipment do you only have to do a insulation resistance test as a miniumum? or do you have to do more to cover the code of practice
Just tested for a new client about 90 appliances.My tester does Class 1/2 and IT.Class III for appliances under 50volts I came across 4 off.2 Laptops and 2 Telephones with transformers etc.The transformers don't have Class III symbols but are under 50 volts.So I always test as IT.
How would you...
I have recently had problems with 3 different RCDs but the problem with each was similar. I was called out to sort trip trouble on an RCD (30mA) in a house, client claming that a chainsaw (class 2) kept triping RCD, however no fault was found. Also the RCD pased all normal tests (trip times and...
nashton
Thread
aus
class
earth
leakage
problem
problems
rcd
socket
Hi - I have an issue with an installation involving a motorised roller blind and would like some advice. I work for a company that supplies motorised blinds and we are being told that a system recently installed does not conform with BS7671 - by the way I'm not an electrician, hence why I need...
Any good? I've stuck with SMA and Fronius so far but I've got a tight budget for a customer. I don't want a false economy but it doesn't need to be bells and whistles either!
Hi -
Got a job coming up in the next week or so were we are installing PV panels either side of Thermal Panels - Do we need to cross bond to the Thermal?
ok my first pir is going ok. COuple of questions to finish ot up firstly there was no earth at a metal light in the lounge as it was twin with no earth replaced for insulated pendant ok for a code 4 now?. The downlights in the upstairs hall are class 2 rated with no earth running to them on twin...
Evening,
I have a class 2 light for the bathroom, and it has its own L & N wires that go into connectors in a type of small chocbox, that go into the loft. Whats the best way/regulation to terminate the incoming earth?
Cheers
changed a consumer unit today from old wylex board to new 17th dual rcd, when i was stripping out i noticed no earth in the lights cable. what would be the best way around this re-wire or can you fit class 2 fittings and switches.
thanks :D
Does anyone have any idea where I can get a light switch (or preferably a dimmer) which is chrome or steel (chrome effect will do I spose) which DOESN'T REQUIRE AN EARTH CONNECTION??? Got an installation with the old no-cpc-on-lighting-but-RCD'd-up chestnut, but the owner really wants metal...
How do you do an earth bond test for these? I have re read the IEE code of practice on this but I can't find an answer apart form: "...can give misleading results"
For example a class 1, totally plastic vacuum cleaner, at least on the outside (it has tiny metal screws not screwed into earthed...
Guys- i have just found a fantastic supply company for all our PV needs.
They will supply all the kit needed to fit PV systems at very good prices( they have big saving offers now), they will even plan your system on PV Sol provided you buy from them.
I have used them a couple of times with...
Just thinking of getting into PAT testing and was wondering if anybody has or can give me advice on what are Class 1, 2 & 3 items? I know what it says in the book but was just interested in what the appliances are, for example what class is a:
Kettle
PC
Monitor
Lamp
Fridge
AC adapter...
Folks,
Doing a bathroom job presently and none of the lighting circuits have a CPC....it's an old topic I know and I'm aware of of requirements so I'll not be fitting that fancy bathroom spotlight!
However, what in theory is wrong with *temporarily* borrowing a CPC from the adjacent...