If I was to install a new shower for someone using an rcbo as theres no rcd protection would this be ok? What i mean is am I ok as long as the circuit I have installed is protected? Or would it be up to me to make sure there was protection for the other circuits?
Hi guys
SWA feeding outside lighting and socket outlets etc.
Set up like this:
Single phase.
L & N T&E out of MCB in main board to feed sperate enclosure with only an RCD module in. So L&N feeding an RCD.
Then, 4 core SWA is glanded to this board.
2 of the cores (L/N) connect...
Unswitched
Thread
4 core
aus
core
cores
electricians' talk
feeding
other
outside
protected
rcd
swa
taken
Installed a garage CU, 2 way. As the house is TNC-S an earth rod has been installed, which is giving an Ra of 102 ohms.
The supply to the garage is protected by a MCB on the non RCD side of the CU, as installation methods don't require RCD protection.
The circuit in the garage has been...
Hello People
A friend of a friend has asked me to put a 150W PIR security light at the back of their house as they believe someone is coming into their garden at night. I said no problem and would just tap into the lighting circuit under the floor boards but they don't want any of the house...
wallyanker
Thread
electricians' talk
floodlight
fused
light
outside
pir
protected
socket
I have a cafe to re-wire and they have 2 freezers that Iam going to wire dedicated sockets for. I dont want to put these with RCD. Will it be possible to use SY cable as opposed to SWA cable will be in plastic trunking surface. I was on the understanding has to be more than 50mm flush, steel...
just having a scan through the examiners notes posted regarding the 2391
noticed on of the comments made was
'
"could not state the minimum test voltage to be used and the minimum acceptable value of insulation resistance when carrying out a insulation resistance test on a circuit containing...
Hi there All,
Why if a Domestic Lighting circuit if feed off the unprotected side of a slpit-board does the RCD on the protected side Open if an upstairs light (dimmer) is cycled on and off 8-10 times? The light of course stays On!
I have checked that the correct number of neutrals match the...
:confused:Hi folks i am soon to be carrying out some work at a beauty salon some extra sockets, lights and a disabled alarm to be added but not nessescary for new circuits, the current wiring not in steel conduit or buried 50mm do i have to change the lighting circuit at dis board to be rcd...
I want to add a light fitting to an existing circuit (installed around 5 years ago).
has one fitting on the circuit at present with an switch in the garage on a 6 amp MCB, tested out fine,
do I have to put an RCBO on the circuitif I add on to it ?
Thanks in advance :confused:
Hi guys my local authority have asked me to carry out some PIR's on some properties with regards to upgrading them to 17th edition. I suspect that the rings will be 2.5 t+e and will have a 1mm cpc, if left will the properties comply with a 1mm cpc using a 32 A mcb (obviously RCD protected) or...
nrbspark
Thread
around
cpc
electricians' talk
installation
mains
protected
result
ring
unsatisfactory
Called to a public council building to carry out a p.i.r on it
Came across disabled shower room with, hand dryer, water heater, and convector heater 3kw all class 1 ,all Supplied by switched fused spurs in the shower room 30marcd protected
style Shower without basin/wet room fig701.1
Now all...
Tapouchoke
Thread
building
calibri
council
electricians' talk
heater
installed
protected
shower
Hi guys I was just thinking about what someone put about a question I asked a couple of days ago. I asked about putting an RCD proceted fused spur on a ring main to feed an outside light. they said the RCD fused spur will be fine as long as its not protected by another RCD on the cu. My question...
eagleeye
Thread
aus
discrimination
electricians' talk
protected
rcd
rcd's
tripping
upstream
Hi all
I've been asked to put in a shower needing a 40 amp breaker but there is only a 30 rcd on the 1 half of the board what is the easiest way of doing this as a freind of mine sid that as long as you have a disconection of .5 secs you dont need to but i cant find anything to confirm this. is...
tommy-trucker
Thread
aus
bathroom
electricians' talk
going
protected
shower
:)can anyone answer this question please !!!!
fuse board is non rcd with 3036 rewirables
job is to run power and light out side !!
Question !!
when taking the feed from the lighting radial or ring final if i used a fused rcd spur to extend the circuits would this be acceptable with...
Hi all,
this is my 1st post and my first electrical job for a while.
I apologise if these questions are simple but i would rather sound stupid and be safe than be quite and dangerous.
I have recently been made redundant and took a course and updated to the 17th and part p(did a 3 yr...
we have a site where in a school kitchen there is a stainless table with just a sandwich maker on it, we are being told enviro health officer said it wants bonding is this correct? the socket is rcd protected.
andyhalf
Thread
aus
bonded
commercial
electricians' talk
kitchen
protected
tables
Hi all im new to the site, hope all ok.
i have just re-wired my garage for the purpose of getting registered again.
The garage is fed from main consumer unitby 2.5 t+e and then joins a swa, which is all existing.
I have re wired the garage, put a 2 way rcd unit in, 1 ring main, 1 lighting...
dbrennan
Thread
additional
circuit
electricians' talk
garage
house
protected
testing
can someone please tell me why when you change an old rewireable fuseboard to a circuit breaker consumer unit does it have to consist of a time delay rcd on a tt system? and also what would happen if you didn't put a time delay rcd in?
wannabesparky
Thread
aus
circuits
delay
electricians' talk
installation
protected
rcbo's
rcd
switch
system
time
time delay
tt system
Does anyone know where i can purchase mk rcbo 6a.No wholesalers have any in stock in the area where i live.Would purchase approx 10 at a time.Thanks in advance.
hen
Thread
aus
electricians' talk
protected
protection
rcbo
using