Just a quick one, got a board change next week and am going to extend everything using an enclosure and din rail etc, normally i just use twin and earth to extend it all but this one as it buts right up against it I was thinking about using singles.
My question is, at what point would you...
Hi peeps
I have continuity measurements on a ring final circuit of: L/L 1.4, N/N 0.78, E/E 1.7
Loose connections somewhere?
There is a new CU with RCD.
Insulation resistance measurements are good.
There is a boiler added into the circuit as a spur.
Any suggestions or comments?
THANKS!!
:) :) :)
Scenario:
In an old house, the main fuse board is next to the supply intake, which feeds sockets, cooker, immersion.
For the lighting, there is a separate sub-board in the centre of the house, fed by a 2.5mm T&E distribution circuit from the main board.
This 4-way sub-board is antique, cast...
Just a quick one.
And I right in thinking I would take N/E from CU in shed to first fitting, take L from CU (with an E from fitting) all the way to switch, run switch L back to fitting and then just Dasiy L/N/E to next fitting?
not a lot of info on the web and didn't cover fluorescent fittings...
Wiring in singles!
working in a commercial building, I have 2 separate rooms and a corridor to wire, the 2 rooms both have light switches and pir's, the same as the corridor. I know how to wire light switches, feed from d/b down to switch, s/l up to pir, then i can wire my lights.
How do i...
Alex2012
Thread
pir
pir's
rooms
separate
singles
switch
switches
wired
I am selling the following. All bought today, I've used just over 6 meters from each roll.
£60 the lot collected from East Manchester or Glossop area. I can give you a VAT invoice that I was given when I bought it for £90 inc.
Prysmian 6491X PVC Singles, all 98.3 meters:
1.5mm Black
1.5mm...
I am doing commercial refurb at the mo, everything is supplied from an old Memshield 3 phase board, the landlord wants the various spaces metered so he can bill the tenants separatly, at present he is just adding a flat rate to the rent, I have no issues with how to go about it however one unit...
hi all first time i have posted, great site and lots of info cheers
putting in for my assesment shortly with elecsa doing a c/u change and putting sockets and lights into attached garage,my preffered method would of been to use 20mm conduit its a pretty big garage but they only want 2 double...
Hi Guys,
I'm a bit rusty but I've just seen single cables installed in a stud partition used for sockets etc. I've never seen this done before but can someone confirm if this is ok?
I seem to remember that they should be double insulated (T&E) or single + mechainical such as conduit/trunking...
Prior to the 17th and the purchase of the 1553 I was using Kew tech singles all good hardly used mint, problem ? = no soft test on the Zs other gear all good, any interest ? how much should I part them out for ?
J
Has anyone ever come across them?
Initially, I was convinced that someone had wired the lighting in this house in SINGLES twisted perfectly together. However on further investigation, it turned out to be coloured, double insulated singles. It looks horendous in the attic, but they tested out...
Morning all been ask to change some light fittings & switch's in a bungalow as the lady said it had just been rewired by the local council and she would like some nice chrome fittings. But the lighting circuit has been done in d/insulated singles with no cpc.
The power circuits are done in t+e...
Iv just been to look at a job in a cafe, the customer needs a cooker circuit and a radial adding the the installation, the 3 phase D-board is in the same room as where the two extra circuits will be.
All the circuits tht are already in this room, radial for boiler and radial sockets feeding...
Hello, can anyone explain the reason for this.
Went to a friends the other day as the RCD was tripping regularly, pinpointed it to a faulty dishwasher, anyway........
Whilst I was there in the loft doing another job, I noticed the lighting was wired in singles, the live and earth loop in&out...
Just calculating my In... conduit with singles run.
For the grouping factor - Cg it states number of circuits
If I have 2 circuits, but this consists of 18 x singles (e.g 1 x ring = 6 and 4 x radials)
Would this still be a factor = 0.75 ?
Thank you
Sy
Have got to rewire a lighting circuit in a flat existing is singles but no cpc. Conduit embedded in concrete
Can i rewire with singles including cpc or have to use t&e
Evening all I was just wondering if anyone can tell me the procedure or a good method for extending a ring main wire in singles the trunking the conduit comes from is innaccessible due to height so I need to thru crimp at outlet one set L,N AND E and connect the other only problem is how can i...
What is the maximum cable capacity (factor) for 200 x 200 steel trunking
2metres up the wall with a 90 degree bend three metres along the wall
And what is the cable factors for 1.5mm and 2.5mm singles
Don't have reference books to hand