HI All
Have just installed a new circuit to supply power to a control panel.
Have tested it all came back fine if i need to carry out a ZE test how can this be done because cannot isolate the main board so cannot disconnect the Main CPC from the MET
Also have only carrird out a ZS at the...
Hi All,
Can anyone recommend a website that provides job leads I have used rated people and myworkman but I never get a response from the customer and often if we call them the numbers don't work. I don't mind spending the money even if we don't get the job I just want the opportunity to...
I have 6 tickets at £25 each if anybody is interested.
Venue is Manchester Platt Fields next Friday (11th June).
All my mates have now decided they can't afford it after I bought the tickets.
If I'm breaking some kind of rule by advertisng these I don't care, I'm a rebel without a cause.*...
Hi all,
just took main protective bond (10 mm) to water pipe which is of the old lead type.
Main bond length is about 4 meters.
Cross bonded to rads and sink(utility sink)
Then did R2(using 2.5mm) to pipes under the kitch sink.
Reading was 0.10 ohms.
regs say max allowed value is...
Mr.Black
Thread
bonding
electricians' talk
main
main bonding
value
On the m.i.c.c cable the 3 phase from the board the resistance between each phase is about 88 mega ohms so think ill get marked dorwn for that also the in the board the conducters are about an inch short of the breaker
the only thing im pleased with is the conduit oh well got another 2 days of...
Jonesy83
Thread
acceptable
am2
cable
electricians' talk
value
you'll
Please forgive my lack of knowledge on this subject.Normally when i have done pir tests i have used the r1+r2 method . To obtain the Zs you obviously use the formula Ze +(r1 +r2 )=Zs example Ze =0.02 r1+r2=0.46 therefore Zs=0.48 I have just been using the R2 method...
I have recently fitted some lights in an attic and when I came to testing found the cpc showing 60 volts. I switched each mcb off in turn and the fault dissapeared when I turned off the downstairs lighting mcb. I am going back this weekend to sort the problem out so will start with an IR test...
yelloperil
Thread
aus
calibri
circuit
earth
electricians' talk
fault
value
Hi All,
Q: If an earth fault loop impedance instrument records a valve of 0.55Ω at 20°c, what is the corrected valve ( Using the rule of thumb method ) to allow for conductor maximum operating temperature?
Any replies will be appreciated.
johnboy1
Thread
earth
earth fault loop impedance
electricians' talk
fault
figure
impedance
loop
loop impedance
question
temperature
value
Am I right in thinking that for any ring circuit the maximum value that r1+r2 can be is 1/2 the loop reading on the phase + 1/2 the loop reading for the cpc ( measured at the CU ) Or has my maths let be down?
Hi all,
Could someone please advise me what the standard procedure would be if you were to get a high Ze reading of 8 Ohms. It was a TNS earthing arrangement. Main earth was upgraded to 16mm, gas and water both verified at 10mm. Im figuring that i will have to liase with the electrical...
I tested a TT system today earth rod impedance was 1467 ohms, I say thats a pass ie, less than 1667 ohms, the QS at work says that it's a fail, it must be less than 200ohms......who's right ??? and why ??:confused:
How do l calculate the maximum cable length for a maximum Zs value?
Isn't there also correctional factors to be applied for ambient temperature? :confused:
Jabbajaws
Thread
cable
calculating
electricians' talk
length
maximum
permitted
value
i'm in year 3 and i'm stuck on a year 1 question, is there any hope for me??
i was wondering if someone could jog my memory on this 301 question please.
question:
A copper conductor has a rho value of 17.5 x 10-9. calculate the resistance of the copper wire if it's length is 20 meters and...
I have a question,
When testing a circuit protected by an RCBO, lets say a type B, in the max permissible column do you put the value from the Regs for the breaker type or 1666 Ohms?
Rang the NIC Tech line and NAPIT's and they both say different.
It's just that if you put the value from the...
Hi everyone
Would be really grateful for your help on this.
I have my 1st NICEIC assessment on Monday (am bricking it) - anyhow I only have an old table & I need one like you get on the back of the proper NICEIC pads - the most up to date table.
Has anyone got one they could send me so...
daz24
Thread
aus
earth
earth fault loop impedance
electricians' talk
fault
help
help please
impedance
loop
loop impedance
max
needed
niceic
please
table
value
Two resistors, when connected in parallel have an equivalent resistance of 15 ohms. If one of the resistors is 60 ohms what is the value of the other?
Question from 2330.
Can't apply 1/Rt = 1/R1 + 1/R2 + 1/R3