Come across an old Installation with 1.5mm CPC on a 6mm Live conductors whilst doing an EICR. Not seen many of these, in everyones opinion perfectly acceptable if all R1 and R2, IR, Measured ZS test check out ok?
 
Assuming this is T&E I have never seen a 6.0 with a 1.5 cpc. The only metric size I know of which doesn't comply to current UK sizing was 1.0 cpc in 2.5 cables in the early 70s.
 
Come across an old Installation with 1.5mm CPC on a 6mm Live conductors whilst doing an EICR. Not seen many of these, in everyones opinion perfectly acceptable if all R1 and R2, IR, Measured ZS test check out ok?

It is acceptable if it meets the required size as calculated by the adiabatic equation and it passes testing.
You must ensure that the size is suitable not just rely on the test results, an undersized CPC could pass testing but melt under fault conditions before the OCPD operates.
 
I find it difficult to believe 6.0 T&E was produced with a 1.5 cpc, four times smaller than the csa of the line conductor.
 
wondering if this was imperial cable ( 7/044 (6mm) or perhaps 7/036 (4mm) ).
 
The OP hasn't confirmed what type of cable it is, I assume it is most likely singles.
Yes I made the assumption T&E in #5 after he used the word cable in #3 but plenty of people refer to a single conductor as a cable so who knows.
 
A quick check in OSG table B7 says it should be fine for typical modern MCBs up to 40A so long as the PFC is below 3kA (and circuits meet the disconnection Zs, of course).

Hopefully the OP can confirm the type of protection meets this sort of adiabatic limit?
 
probably alot of the time you can go very small with the adiabatic equation but it's not great is it, if you have have such a small cpc for a large current carrying cable - before the protective device operates is it really going to be the path of least resistance compared to your body?

and if the protective device is slow or fails, it's going to burn up pretty. quick.
 
probably alot of the time you can go very small with the adiabatic equation but it's not great is it, if you have have such a small cpc for a large current carrying cable - before the protective device operates is it really going to be the path of least resistance compared to your body?

and if the protective device is slow or fails, it's going to burn up pretty. quick.

Yes it will be a path of lower resistance than your body,

If the protective device fails then any CPC will melt, unless you size it bigger than the line conductor as then the line conductor will melt.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Dronfield
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
1.5mm CPC on 6mm Cable
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
briefcasedan,
Last reply from
davesparks,
Replies
12
Views
3,031

Advert

Back
Top