Come across an old Installation with 1.5mm CPC on a 6mm Live conductors whilst doing an EICR. Not seen many of these, in everyones opinion perfectly acceptable if all R1 and R2, IR, Measured ZS test check out ok?
I find it difficult to believe 6.0 T&E was produced with a 1.5 cpc, four times smaller than the csa of the line conductor.
Yes I made the assumption T&E in #5 after he used the word cable in #3 but plenty of people refer to a single conductor as a cable so who knows.The OP hasn't confirmed what type of cable it is, I assume it is most likely singles.
probably alot of the time you can go very small with the adiabatic equation but it's not great is it, if you have have such a small cpc for a large current carrying cable - before the protective device operates is it really going to be the path of least resistance compared to your body?
and if the protective device is slow or fails, it's going to burn up pretty. quick.