Awful lot of copper on show in the mcbsEvening All,
I attended a job today to disconnect an Alarm System at a ground floor flat. On taking the consumer unit front off, discovered the incoming neutral tail to be 11 x 1.5mm single core cables which needless to say aren't all tight and secure in terminals. The incoming line looks to be 25mm 6181y albeit without the grey sheath. The main earth is 4 x what looks like 4mm solid core. They all come into the board in 1 grey sheath then split off.
Traced back, at some point in the flats roof it connects to an SWA ( point of connection is not accessible ) then back to a switch fuse with 80a fuse.
I dont think its an option to run any new cables ( which is my ideal method to sort issue) as its all in ceiling void with no obvious access but I am exploring this possibility with the flats owner/ building maintenance people.
The only option I can think that might help is heat shrink round the cables and ferrule the end but im not really happy with it.
Has anyone seen this before? Any ideas what's the thinking behind it? And what I can do make it safe?
View attachment 62156
Awful lot of copper on show in the
Me too. In 21 years I've only seen it once, when I mistakenly flagged it on an EICR.Amazing that I've probably changed 300+ consumer units. Attended 1000's of jobs so looked in nearly all of those consumer units. All jobs around the county Nottingham, Leeds, Stoke on Trent, Stafford, Birmingham, Leicester, Coventry, Derby, Northampton and never seen split concentric used at all. And only ever heard it used by DNO. Cray Cray
I’ve come across this couple of years ago. It’s to do with harmonics this install is most often used in residential block buildings where supplies are run together and apparently reduces harmonic distortion baffled alsoDNO supplies for PME systems will use a concentric cable where you have the phase core and a single PEN surrounding it. Split concentric as in this case have the phase core and separate neutral and earth surrounding it, not normally used by DNOs but is used for SNE supplies (Separate Neutral Earth).
I seem to remember that solder isn’t permitted in this situation, or maybe that’s for tri-rated conductors?I was just about to ask how people wire all these 11 wires into something until you put this. I was going with the same idea as yours but then to add solder to it as well, so that you get a better bonding. Not sure if that's over the top...
I seem to remember that solder isn’t permitted in this situation, or maybe that’s for tri-rated conductors?
Strange isn't it. I think for me it may be because i havnt worked in a lot of flats. Maybe only 50 ish, 99 percent is either houses or commercial unitsMe too. In 21 years I've only seen it once, when I mistakenly flagged it on an EICR.
Thank you. The N wires in split con are solid, so it looks like solder can be used.
Doesn't the reg also say multiwire? I'd say that would include the split concentric neutrals.Thank you. The N wires in split con are solid, so it looks like solder can be used.
(But it shouldn’t be necessary )
Thank you. The N wires in split con are solid, so it looks like solder can be used.
(But it shouldn’t be necessary )
Doesn't the reg also say multiwire? I'd say that would include the split concentric neutrals.