I found that you need to test each 100mA 'S' RCD with each 30mA RCD/RCBO combination to find out the precise time they disconnect. We know at 1 times they should operate between 130ms to 500ms and at 5 times they should operate between 40ms and 150ms but it is not always the case that discrimination is can be achieved.

The 4293 RCCBs have a lower front end of 200ms and maximum of between 300 and 400ms and often only trip near the maximum time allowed.
 