jon4381

Hi everyone, can someone just clarify something for me. When using a 110 volt 32 amp extension lead, what size cable would you expect to see.
 
you'd probably get away with 2.5mm in free air.
 
Thanks telectrix, been doing some pat testing off shore on wind turbines and from what I can see the maximum 2.5 cable can take is 27 amps. Am I missing something here.
 
hint. ref; method E. alternatively, get manufacturers data on the cable. yo'ull find that flex, being multi fine strand will probably withstand a higher loading than the figures given in BS7671.
 
"110 Extension Leads" what do you want that many for?? I hope you are not planning on daisy chaining them! LOL.
 
It just seems a bit to close to the amp rating. When we all know they will daisy chain them and that will in turn compromise the disconnection time.
 
a problem you may find is that the only fusing is on the primary ( 240V ) side of the transformer. to cope with inrush, this will probably be a 32A C type MCB.and that's for 1 transformer. if you have several transformers running on 1 circuit, then the OCPD rating will do nothing to protect the 110V cables.
 
that's because all the power is being used to turn them offshore fans.
 
I personally think it would be the other way round the house would be powering the wind turbines , im sure its a only matter of time before a ship hits one of the hideous things off the north wales coast
 