Hi all,

I went to a property to replace a dining room light which was not operating.

The dining room had two switches which both switched 1 light on/off.

I tested for voltage at the light and noted when switched on that 230v AC was present.

When off 110V AC was present.

Any ideas? Thanks in advance.

Andy
 
What did you measure the voltage with? And was the 110v L-N, L-E, N-E?

If the instrument you used has a sufficiently high input impedance, there will be minimal current flow and the voltage could simply be an induced voltage on the cable (either from inductive or capacitive coupling when running next to other cables).

If you used an AVI they typically have a much lower impedance meaning a greater current will flow and the voltage will disappear if it's induced in some way.

Failing that, sounds like you should be giving that circuit a thorough test starting with continuity (looking for bad joints) and IR.
 
What did you measure the voltage with? And was the 110v L-N, L-E, N-E?

If the instrument you used has a sufficiently high input impedance, there will be minimal current flow and the voltage could simply be an induced voltage on the cable (either from inductive or capacitive coupling when running next to other cables).

If you used an AVI they typically have a much lower impedance meaning a greater current will flow and the voltage will disappear if it's induced in some way.

Failing that, sounds like you should be giving that circuit a thorough test starting with continuity (looking for bad joints) and IR.
Beat me to it with the first part. Agree with the rest though.
 
The dining room had two switches which both switched 1 light on/off.
I tested for voltage at the light and noted when switched on that 230v AC was present.
When off 110V AC was present.
Hi - 230V must be present on at least one terminal of one switch. Then the switched terminal is either 230V when the switch is closed or when it's OC the terminal may float, depending on connected load. Hope that helps :) .
 
I hope you don't think I am being disrespectful here, but your profile says you have a HND in Electrical Engineering, plus a C&G qualification in Inspection and testing. I presume you are a Sparky as you say you "went to property to change a light switch", so I am just curious to know how do you manage to get through the day if you can't sort out a simple 2 way light switch problem?
 

Reply to 110V present with light switch off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Double pole switches? Mounted on a grid module? Ignore the fact they have a N stamped on them. Or is your 2 gang switch decorative, and you...
Replies
3
Views
544
  • Question
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
Replies
1
Views
663
  • Question
Ah OK, that makes sense. Thank you Avo.
Replies
12
Views
2K
Thank you for your response. I really appreciate it.
Replies
13
Views
621
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks