G
guest119
A question that divides myself and a colleague.
A 230/110volt wall mounted transformer feeds a 2 way 110v DB fitted with DP MCBs for the outgoing ways.
The outgoing radials each go to a 16a wall mounted 3pin yellow/110v sockets.
The installation is of metal trunking and steel conduit therefor wired in singles.
What colour are the singles to be, excluding the cpc?
I say brown/brown.
Boydy
i would say brown/brown.....once you go through a transformer, you loose the neutral, so therefore its L1 & L2 out
Hang on a min.
There is a 110 db after tranny so there is a neutral from there so brown and blue
No, DP RCD's. As it should be for centre tapped 110V.
I'm sticking with convention Red/Red (I'm older than most of you). Brown/brown if we have to be posh.
No such thing as a neutral on a reduced low voltage system with centre tapped earth. It's line and line, even at the 110V DB. RLV Uo is 55V so it cannot be classed as ELV, therefore it is still LV and bound by the same rules for LV ac circuits. Line conductors are to be brown in colour.
Even if transformer was a one to one (230v to 230v) the output would still be 2 lines out, with no neutral
Yes, these are called isolation transformers and provide electrical separation. You are correct, both line conductors would need to be brown as there is no neutral.
Probably teaching you how to suck eggs I know :D