If one of the 110v conductors was Blue, then there would be 55v between the Apparent Neutral (Blue) and earth.
Neutral to Earth 55v,, Potentially an incident waiting to happen.
I say brown/brown.
You are correct. There is no neutral in the Reduced Low Voltage system.
It always irritates me with RLV extension leads where they have "wiring instructions" fitted saying line brown and neutral blue.
Doesn't give you much faith in the manufacturer if they don't know that there isn't a neutral, does it?
Yes, these are called isolation transformers and provide electrical separation. You are correct, both line conductors would need to be brown as there is no neutral.
Probably teaching you how to suck eggs I know :D
Not quite correct, it depends if one of the secondary side legs, has been grounded or not. It may well be that the TX is supplying an independant earth system. I can think of one or two scenarios where that would be the case...
Surely that would only be in a step up/down tranny? The only reason for 230V in - 230V out would be electrical separation.
If im worng explain a scenario where you would install an isolation transformer for any other purpose?
I'm not having a go, I'm actually interested.
As in the other side of the TX has it's own earthing system, the isolation being (depending on what type of isolation TX has been used) for elimination of capacitive DC currents, and dirty/noisy voltage. Very similar arrangements can be found on the larger IT or other system UPS isolation TX's, again depending on what earthing arrangements are made in the computer suites etc...
I remember once in Malaysia, a river ambulance attached to the 150 bed clinic i was working on. A single phase isolation TX supplied the ambulance with shore power, which served two purposes to supply clean voltage to the boat, and to stop galvanic corrosion of the hull. eg one leg of the secondary winding was earthed via a connection to the hull, which basically provides a standard TN supply...
I'm not saying that your not correct for normal everyday isolation TX installations, just that there are instances out there where you would be earthing a winding leg thus creating for all intent and purposes a ''Neutral'' connection, rather than 2 X lines...
Sorry for taking a bit of time replying, had some company pop round, still here actually!! lol!!
Ok, yeah, I see what you're getting at, but you're still operationg off an electrically separated supply albeit reverting back to ADS. You are correct though, if this was it's purpose, it wouldn't be an isolation transformer providing electrical separation :)
yawn , daytime forum chatter is as exciting as daytime tv.
im actually looking foward to antiques programs such as cash in the attic after reading about isolating transformers.
:-D
Would have thought, taking one leg down would only be an isolated line.........and only if like sub tx, we took the center tap, back to earth would we then have the center tap as our new neutral and each leg would be still line outs.....basically we have two phase/neutral setup......
Sure it's still an isolation transformer, input and output are totally separated/isolated as is any earth connections on the primary side from the secondary side. Safety screening between the cores is connected to the primary earth to ensure that fault currents (say from insulation breakdown) operate OCPD's on the primary side. In effect, the isolation transformer recreates a totally isolated AC supply....
Talking about Genny's, how did you get on with the manufactures today on your Genny project??