Yes I have two cables in the MCB and I have had the floor Boards up in the room as I was going to add the sockets myself, it’s definitely two radials.
You say there is one 16A Mcb controlling two radials, each circuit should have its own mcb.
 
These either need to be split into their own mcbs or if possible be made into a ring and put on a 32A mcb,
IMO get an electrician to check the installation for you they have the right equipment to ensure yours and your families safety.
 
Last edited by a moderator:
You say there is one 16A Mcb controlling two radials, each circuit should have its own mcb.
not necessarily. 2 radial branches from a single MCB become 1 circuit, although separate MCBs would be an improvement due to separation of circuits reducing inconvenience if the was a fault on 1.
 
not necessarily. 2 radial branches from a single MCB become 1 circuit, although separate MCBs would be an improvement due to separation of circuits reducing inconvenience if the was a fault on 1.

Thanks tel,
I’ve always thought that if you have 2 branches from on mcb being a radial the additional branch may only serve on point as per the “spur off a spur”? As these radials will have more points that is why I suggested the the two mcbs.
 
no. a spur is only relevant to a ring final. that's because it's a single 2.5mm cable fed from a RFC and protected by a 32a MCB, when that single cable is only rated at 27A max. you can have several radials off a 16A or 20A MCB as that MCB has a In < the Iz of the cable/s.
 
Between £450 and £600 for a board change.
You've got 2 boards so maybe £650-£800 plus any costs to bring up to speck on any anomalies on the testing.

I wouldn't be changing those except removal of MCB's and replacing them with RCBO's ........... on the circuits that need RCD protection
 
These either need to be split into their own mcbs or if possible be made into a ring and put on a 32A mcb,
IMO get an electrician to check the installation for you they have the right equipment to ensure yours and your families safety.
This is my thoughts as well was just going to post the same.
 
Beer free assessment, although I'm drinking a strong coffee; I would forget about the extra sockets for the time being, save up my pennies and get that mess sorted out. I dare say the rest of the install needs some tlc.
 
And who would take a chance pressing that ‘test button’ probably not reset - like the old VOELBs
 