HappyHippyDad

-
Esteemed
Arms
Reaction score
5,604
Afternoon all..

A couple of questions..

I shall be installing an 80A switch fuse after the cut out as both the supply and the CU are being moved and they will be greater than 3m apart. There will be approx 2m of tails on the outside wall in conduit and the remainder (approx 8m) will be between the floorboards (without insulation)

1. I am planning to use 25mm tails simply because this is recommended by the on-site guide and for rewires this again seems to be the recommendation, or rather the 'good practise'. My question is why would 16mm tails not be acceptable? If reference method C is used then 16mm has a CCC of 87A, also I believe the voltage drop is ok given a max demand of 80A (haven't got the tables to hand).

2. I can see where the incoming supply cable enters the house so I want to install and position the new meter box myself so that the DNO will have to 'shorten' their supply cable rather than joint it. The reason I want to do this is because I want to get my switch fuse in the new meter box before they fill it up, as they may not position the meter and cutout with my switch fuse in mind, whereas I will consider their needs.
Is it ok for me to install the meter box and pop my switch fuse in before they do there bit?

Cheers.
 
Last edited:
1. Come on HHD this is a simple calculation.

2. Phone them and ask them.

1. I know the CCC works out fine Dillb (although in conduit (ref method B) the CCC drops below 80A) and the volt drop is ok, but wherever I look it states 25mm and I just wanted to know why? I suppose because of what could be added on at a later date. I'm going to install 25mm as I dont want any trouble if the assessor chooses this install to see (and the fact that for 2m the tails are in conduit and will have a lowered CCC (below 80A)).

2. I was/am going to do that Dillb, but not until monday so i thought I'd see what you guys do. I expect the fact that it involves the DNO will mean that sometimes its fine, sometimes its not :smile:
 
Last edited:
I say that what you're installing is a distribution circuit, not 'tails'. The tails are just the section between meter and switch fuse. So you just need to design your distribution circuit, including its overcurrent protection (your switch fuse), in accordance with the usual circuit requirements.
 
2) In my limited experience on this subject, my DNO expects the customer to supply the meter box and fit it as well. And although they don't own it they have certain requirements, like only our equipment can go in there. But when I spoke to them about fitting switch fuse in there, in similar circumstance, they were okay with it. Best to give them a ring/email and agree what they deem acceptable, before their guys turn up on site.
 
Which dno is it? You normally get a guide telling you exactly what they expect you to do before they arrive.

The basic idea is that you fit the meter box, the left hand side of the back board is reserved for dno equipment and the right hand side is for the consumers equipment. You got whatever you need and leave your tails ready for them to connect.
 
Which dno is it? You normally get a guide telling you exactly what they expect you to do before they arrive.

The basic idea is that you fit the meter box, the left hand side of the back board is reserved for dno equipment and the right hand side is for the consumers equipment. You got whatever you need and leave your tails ready for them to connect.

Western Power.
The client hasn't received the pack yet.
 

Reply to 16mm or 25mm tails plus when to install switch fuse? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
758
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
I’ve got a job to quote for turning 1 big flat into 2 smaller flats. The DNO are looking at installing new meters in the communal area. I need to...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock