Hi Everyone,

Just a quick question, in the 18th edition wiring regulations book page 483 the schedule of tests results form it shows IR tests Live-Live & Live-Earth
Are they now going away from the Line-Neutral, Line-Earth & Neautral-Earth & just doing the combined test?

20190114_090656.jpg



Thanks

Michael
 
it's that N is now classed as a "live" conductor. so yout L-L column would be L-N and L-Ewould be the lower or the readings L-E or N-E.

confused? you will be.
 
true, but sheet says live-live, not line-line.
 