Had these on the 18 th exam,confused me a bit.
What’s the maximum Rcd that can be used ,when an Earth electrode Reading is 2 ohms.
100 ma
300 ma
30 ma.
What would you say is the answer.
 
with a fault current of 115A, what do you think will trip i 200mS or less?
 
300mA , but somewhere I recall BS7671 or a GN recommending 100mA for a TT installation ( presumably to allow for variations in the Ra)
 
Is that actually a genuine 18th Ed question or something from online.
 
Could they be relating to this table on page 64

20181124_081346.jpg


but from memory i thought you used a 100mA RCD on TT & then 30mA at board.
 
now that is interesting. the bit about insulated and sheathed cables meeting the requirements of double or reinforced insulation.
 
Yea,I actually ticked the 300 ma,being the max,obviously the ideal would be the 30ma.
nope. you'd have 30mA for final circuits. if you had a 30mA for fault protection, that would contravene the division of circuits and discrimination of RCDs in series.
 