Had these on the 18 th exam,confused me a bit.
What’s the maximum Rcd that can be used ,when an Earth electrode Reading is 2 ohms.
100 ma
300 ma
30 ma.
What would you say is the answer.
 
300mA , but somewhere I recall BS7671 or a GN recommending 100mA for a TT installation ( presumably to allow for variations in the Ra)
 
Could they be relating to this table on page 64

20181124_081346.jpg


but from memory i thought you used a 100mA RCD on TT & then 30mA at board.
 
Yea,I actually ticked the 300 ma,being the max,obviously the ideal would be the 30ma.
nope. you'd have 30mA for final circuits. if you had a 30mA for fault protection, that would contravene the division of circuits and discrimination of RCDs in series.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
18th edition question
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
Ffoeguk,
Replies
26
Views
3,059

Advert

Back
Top