Marvo
Yeah its in my own house.
2 holes isn't practical due to ladder position restrictions but could be done if required.
Just after easiest option
I've also read that it needs to be pretty powerful for 2 rooms.
Any idea on the rate required for 2 rooms?
You can use 2 fans into a common discharge duct but you should go up at least one duct size after the point they join and you would need inline shutters on both rooms. You can also go with a common fan for both rooms but the wiring can get a bit tricky depending on existing layout and you'd need an adjustable diffuser in at least one of the rooms to give you some adjustment on the air balance. The room with the shower I'd be working on at least 20 room volume changes per hour and probably 15 changes on the other room.