Yeah its in my own house.

2 holes isn't practical due to ladder position restrictions but could be done if required.

Just after easiest option :)

I've also read that it needs to be pretty powerful for 2 rooms.

Any idea on the rate required for 2 rooms?

You can use 2 fans into a common discharge duct but you should go up at least one duct size after the point they join and you would need inline shutters on both rooms. You can also go with a common fan for both rooms but the wiring can get a bit tricky depending on existing layout and you'd need an adjustable diffuser in at least one of the rooms to give you some adjustment on the air balance. The room with the shower I'd be working on at least 20 room volume changes per hour and probably 15 changes on the other room.
 
Have you considered using PIRs to control the lights?? That makes them independent of the fan and each other.
 
or one of these .

The vents would look lovely

10940561_10155118312135581_796566869034476353_n.jpg
 
Why don't you fit 1 in-line fan in the loft and just put vents in the two rooms. Wire it so either light turns on the fan. Plus the extract will be very good.
 
Why don't you fit 1 in-line fan in the loft and just put vents in the two rooms. Wire it so either light turns on the fan. Plus the extract will be very good.
Would that just require a switch wire from each light to the fan?

I've read about relays being installed.
 