What range of accessories has a socket plate with large capacity terminals? I am about to run a 10mm2 SWA cable to a shed and the customer has asked if I can put a couple of sockets in weather-proof enclosures along the route. Can any socket's terminals take 2 x 10mm2 or must I do some clunky choc block lash up?
You're not frightening me.....but someone's up for grabs.
Oh Dear.....Just get someone to do the work that actually know what they are doing
thinl it would need the SWA glanding into and out of an external double socket back box and tapped off to socket with 6.0mm tails.
I personally wouldn’t cut the s.w.a , Take it as one piece length all way down to the shed end and terminate in the consumer unit . Are you sure you require 10mm I almost always exclusively use 4mm or 6mm for shed hook ups (2.5mm if it’s just a socket and light).
Anyway back to the question... then just take some 2.5mm s.w.a feeds from the shed to feed some exterior sockets.
Much easier to terminate
??????????????????? are you hopefully not as they say part p?
I think for your first post it would have been better to avoid the term 'clunky choc block lash up'. This site tends to pick up on wording like that and then the advice given may not always be too polite.
I would question whether it needs 10mm cable. As others have said 4mm or 6mm is usually fine, although we would need to know the length of the run and the max demand of the shed to be certain of this. This would then solve your problem as you can definitely fit 2 x 4mm in a weatherproof socket (and probably 2 x 6mm although I have never had to do this).
If you do need to use 10mm then rather than a 'clunky choc box lash up' in the back box of the weatherproof socket you could have a weatherproof adaptable box next to the socket which you terminate the 10mm into (and out of) and then some 2.5mm H07RN (basically black rubber flex) going into the weatherproof socket.
Of course the OP may be using 4 core 10mm2 SWA as he needs to bond something in the shed! Doubtful but possible.
Do give us some more details Lord Buncefield and don't be put off writing again just because some take the mickey. Just read the useful replies :)
You are not going to get 2x 10mm conductors in any 13a socket terminations. If you propose to use the 10mm supply cable in the way stated you will have to run it through a separate enclosure, terminate and take a smaller cable to each socket. However your method begs the question as to whether the 10mm is intended to be a distribution circuit feeding a DB at the shed end with RCD protection there, as it would now be a final circuit requiring RCD protection at source.
Reply to 2 x 10mm2 into socket terminals. in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Completed a new install recently. 45a 10mm2 SWA Sub main (TT) to an outbuilding and 2 x final circuits- 32a Ring and 6a lighting, nice and simple...
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...