Questions to the OP:
What size OCPD is protecting this cable?
How long is the run?
Is this cable protected by an RCD?
Why have you opted for 10mm2, have you done any cable size calculations?
What installation method are you employing?
That's about it I think.
I think you hit the nail on the head in your post-No.3 Pete with the 20A radial from the shed to the sockets or from the house end.
You are not going to get 2x 10mm conductors in any 13a socket terminations. If you propose to use the 10mm supply cable in the way stated you will have to run it through a separate enclosure, terminate and take a smaller cable to each socket. However your method begs the question as to whether the 10mm is intended to be a distribution circuit feeding a DB at the shed end with RCD protection there, as it would now be a final circuit requiring RCD protection at source.
or he could fit IP65 RCD sockets, not sure if that would be allowed tapped into a distribution circuit. is there a reg. prohibiting that?
No you are right, he could do that....cant think of anything that would prohibit it, but as others have stated, the best option would seem to be a suitably sized final circuit coming back from the shed.
Originally, I thought ‘What a nasty forum – if this is how you welcome a newbie, I’m out of here’. Then I realised it was Friday night and a few beers might have been consumed after a tense working week. That may have been the reason but was not an excuse.
Thanks to those who made on-topic, constructive responses.
The outbuilding is to be a pottery studio and will have lights, a socket ring and heater spur (but no kiln, thank God) and is 50m from the origin CU, therefore the calc is just into 10mm2 to avoid excessive volt drop.
This new submain would share half of a split board (large house) and outdoor stuff is always at risk of tripping an RCD. A mate has advised me to give the shed and outdoor sockets a dedicated RCD/RCDs and also that I would have a distribution circuit doubling as a final circuit and it should be one or the other (as per Wirepuller).
I spoke to the customer yesterday to urge her to let me feed one outdoor socket from the shed mini CU (local RCD) and the one nearer the house (25m run) from an RCBO in a new mini board within the house. It’s a lot more cost and if she doesn’t buy it then I will have to cut the 10mm2 and put sockets on it as per plan ‘A’.
No don't revert to Plan A M,Lord, it's the wrong thing to do.
I personally wouldn’t cut the s.w.a , Take it as one piece length all way down to the shed end and terminate in the consumer unit . Are you sure you require 10mm I almost always exclusively use 4mm or 6mm for shed hook ups (2.5mm if it’s just a socket and light).
Anyway back to the question... then just take some 2.5mm s.w.a feeds from the shed to feed some exterior sockets.
Much easier to terminate
The trouble is the socket and light in the shed in most cases always morphs into something bigger than was originally intended
So how do you intend to get two 10mm cables into a socket you can only get two 6mm in at best on the sockets that have larger bellmouth terminals What is the design current plus protective device are you using as socket-outlet terminals are only rated at so much.
You may well have to use that swa to feed 3 distribution positions,the shed at the end and each socket position otherwise a troublesome socket problem could well end up knocking the innocent shed off power if you revert to plan A
I think the 2 socket positions would at the minimum need a double pole isolator and a mcb housed in a weatherproof unit
By the time she would pay for these, the swa from the shed will seem like less of a cost heart attack to her
just daisy chain a bunch of these into a 13 amp fcu :)
wickes.co.uk/Masterplug-Weatherproof-Garden-Spike-Lead---15m-10A/p/117877?utm_source=google&scid=scplp117877&sc_intid=117877&gclid=EAIaIQobChMIspWUkJXH4wIVg7TtCh02TwySEAQYBCABEgIu5PD_BwE&gclsrc=aw.ds
Don't feed sockets directly from the distribution circuit like this, there's no regulation about it because the people who write the regs don't expect anyone to be so daft that they need to be told it's a bad idea!
"a mate has advised me" is a worrying thing to state, if you are designing the installation then you should have sufficient knowledge of the regulations, or at least he able to read up on the relevent regulations to do the design.
If this distribution circuit is going to be on an RCD protected way in a CU then it's a terrible design and pitting extra RCDs after it will achieve nothing.
I still stand by my post and believe you need to get someone who knows what they are doing to do the work safely......also you as the electrician should advise the client how the work will be done and not the other way around...... and by the way I don't drink
Totally agree
Get someone in who has the knowledge and experience to design the installation. And I would say by original post that this is a new circuit and would need certification. And not being nasty but by the original question is the person competent to initial test and verify the circuit and issue paperwork under part P ?
Reply to 2 x 10mm2 into socket terminals. in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Completed a new install recently. 45a 10mm2 SWA Sub main (TT) to an outbuilding and 2 x final circuits- 32a Ring and 6a lighting, nice and simple...
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Electrical2Go - A Guide to Click Sockets: Which Is Right For You? Click Sockets Guide: Which is right for you? Click is a leading manufacturer...