Can a 2kw (on a 1.5mm manufacturers flex) fitted oven and a 6kw hob (on a 2.5mm manufacturer's flex) be connected into a cooker outlet plate behind the cooker? The circuit is wired in 6mm t&e on B32 mcb. It has a 45A cooker switch with 13A socket in the kitchen (within a metre of the appliances)
 
Yes you can - but - I think you will need to connect both supplies to FCU's below the outlet. Otherwise you'll have a 1.5mm2 cable (max current carrying capacity 16 A) and a 2.5mm2 cable (max current carrying capacity 25A) only protected by a 32A MCB
 
Yes you can - but - I think you will need to connect both supplies to FCU's below the outlet. Otherwise you'll have a 1.5mm2 cable (max current carrying capacity 16 A) and a 2.5mm2 cable (max current carrying capacity 25A) only protected by a 32A MCB
As these are fixed loads there’s no risk of over current so no requirement for local fusing down. Also I don’t know of any 26 amp FCUs.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
2KW oven and 6KW hob on B32 MCB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
JimmyG,
Last reply from
Strima,
Replies
7
Views
4,500

Advert

Back
Top