Is there an existing distribution board in the new building?
No its a new building, there was a mobile unit there a few years ago but there was just a cable left over. This building is meant to be more permenant. The cable was just disconnected in the main building DB. It runs under a playground so theres no chance of running a new one or thats the route i would have gone. I've been asked to reinstate the cable and fit a new DB plus a few sockets, lights and water heater for the toilet.
 
So is main protective bonding required.
 
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.
 
  • Like
Reactions: Simon-0116 and DPG
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.

There is no seperate CPC. The SWA is earthed but i wasnt confident in using this as a main earth for the installtion of the building because of the join.

If you are concerned that there is a problem with the joint cut it out and re-joint the cable properly.
 
  • Agree
Reactions: TimaT

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 phase supply to classroom, unsure to TT?
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
46

Advert

Thread statistics

Created
mpoy222,
Last reply from
davesparks,
Replies
46
Views
6,068

Advert