just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance, separate circuits, b20 mcb warehouse). I used these energy efficient timer switches to save energy. I have managed to get the wires in but it’s tight, I feel if I remove the cover it pull the connections out from circuit board inside. Thinking about ditching the switches, any ideas what I could. I don’t want a metal glad switch in case people forget to switch it off.


Eterna IP66 16A Electrical Outdoor Time Delay Switch (Switch I installed)​


Thanks
 

Attachments

  • IMG_3996.jpeg
    IMG_3996.jpeg
    575.2 KB · Views: 85
small board with some contactors in it close to the source of supply.
then you only need 4 core +E in a small size to run from the board to the switches.
 
I doubt the terminals in those are suitable for 4mm, more likely designed for 1.5mm as they are limited to 16A.

You could use the time switch to operate a contactor to switch the actual load, either one contactor to switch all 3 at once or individually. Thai has the added advantage of reducing the load on the timeswitches and potentially extending their lifespan.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
3kw heaters install, timer switches
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
James2249,
Last reply from
davesparks,
Replies
2
Views
997

Advert