newfutile

~
Arms
It's coming out anyway so it's a rhetorical question.
What do you you all think of this?
Bits of wire used to bridge the bus bars and don't single phase consumer units need a linked switched line and neutral?
Screenshot_20230510_102812_Gallery.jpg
 
Briefly - IMHO the question is more about the size of the links.
See section 460 regarding need to isolate N
 
Poor practice to have used cable and not bus bar due to the risk of overload, no requirement for interlinked switch to disconnect the neutral unless it's in a domestic-ish setting (462.1.201 & 463.1.2)
 
Last edited:
Have seen this done quite a few times where some off cuts of cable have been used to link across the main switch.
Like wise have come across a fair few domestic boards where the busbar has been lost and they have linked out the bottom of the MCBs in 2.5 cable
 
Hager also do a 4P incomer switch kit so you can have both the single-phasing kit and DP isolation if you do it right. Not like here!

But I do wonder WTF was anyone fitting such a small 3P board for SP use?
Ordered a 4 way board, without paying any attention to detail, and made the most of what turned up?

Edit: I can see 6 breakers, but liked the idea.
 
Ordered a 4 way board, without paying any attention to detail, and made the most of what turned up?
Could be. I did wonder after posting if it was anything to do with needing industrial levels of dust, etc, tolerance or even 10kA break capability.

Then I remembered the wires and clearly they were not design considerations...
 